Twin/Dual Induction hob
#16
Re: Twin/Dual Induction hob
If the hob is rated 3500 watts, that is maximum demand if all features are on at 100%.
Circuit breakers have trip curves - they should not trip at rated value, but will instantly trip at 3 to 5 times for B type breakers (5 to 10 times for C type).
You can google the trip curve for your breaker, but it will likely carry twice the rating for almost a minute.
Assuming the wiring is adequate - at least 2.5mm.
Anyone still having old school fuses should consider replacing them - and also look to have socket outlets / lights protected by RCD's (protection from earth faults).
Circuit breakers have trip curves - they should not trip at rated value, but will instantly trip at 3 to 5 times for B type breakers (5 to 10 times for C type).
You can google the trip curve for your breaker, but it will likely carry twice the rating for almost a minute.
Assuming the wiring is adequate - at least 2.5mm.
Anyone still having old school fuses should consider replacing them - and also look to have socket outlets / lights protected by RCD's (protection from earth faults).
#17
BE Forum Addict
Joined: Nov 2012
Posts: 2,096
#18
Re: Twin/Dual Induction hob
We're nowhere finding an architect and we really need the kitchen updated. I think it's commonsense to build new extension, them update kitchen and add fittings to the extension. But ... as mentioned ... there may be some delays before any work starts so despite my wife doing a brilliant job cooking with a Ninja 9 in 1, microwave and an additional slow cooker we have I thought maybe we should buy an electric twin/dual induction hob to make things a bit easier. I think eventually she will start to get tired of balancing things, hence the induction hob.
Looking at the wattage ... a twin/dual uses 3500 watts. Will there be a problem plugging into a normal socket?
Looking at the wattage ... a twin/dual uses 3500 watts. Will there be a problem plugging into a normal socket?
https://www.alza.hu/sencor-scp-2254bk-eue4-d6362992.htm
#19
Re: Twin/Dual Induction hob
For the hob - agree with checking what else is on circuit - and limit power setting to 90% if 1.5mm wiring (or less if other devices on circuit need to be powered). That should be achievable by turning one side on first and waiting to at temp before using second side, or not using at highest heat setting if variable.
Fuses can take longer to blow under fault conditions - and may not blow at all with 1.5 to 2 times rating (or even higher depending on type) which leads to damage to the wiring. Always better to upgrade to MCB's for that reason.
#20
Re: Twin/Dual Induction hob
For the time being why don't you buy a double plate electric hob? I used one for years when I lived in an apartment with a tiny kitchen. I also had a small DeLonghi table top oven and a microwave and could easily cook a meal for four people.
https://www.alza.hu/sencor-scp-2254bk-eue4-d6362992.htm
https://www.alza.hu/sencor-scp-2254bk-eue4-d6362992.htm
#22
Banned
Joined: Jul 2014
Location: Hawley
Posts: 958
Re: Twin/Dual Induction hob
Moderator The link is NOT intended to sell or endorse a company, It is only posted for informational purposes regarding electrical theory and calculation in regards to electrical current requirements and use.
https://www.fluke.com/en/learn/blog/...at-is-ohms-law
#23
BE Enthusiast
Joined: May 2015
Location: Near the Black Forest and near Esztergom
Posts: 923
#24
Re: Twin/Dual Induction hob
But suppliers have tolerances on that - and there are slight differences on that depending on nominal values before the change.For most of Europe (the former 220V nominal countries), these limits are -10% / + 6% or 207.0 V / 243.8 V and effectively the harmonisation is a label change, not a value change. (For the UK (previously 240V nominal) the limits are reversed: -6% / +10% or 216.2 V / 253.0 V.)
Power ratings are current x voltage (there are other formula, but this works.) so for 3500 W, at 220V current is 3500/220 = 15.9 Amps (and for the 2500 W hob, current would be 11.4 Amps).
So at 220V, current is a little higher using this calculation but not significantly - and the initial power rating may be based on the nominal 230V value anyway.