peer exam 25th &26th May
#1
peer exam 25th &26th May
Hi,Finally booked up the test after months of looking through this bloody workbook.Still struggling on cable selection and vd.Ive heard the examiner is very helpfull over in adelaide,so hopefuly sort it out there.
Anyone know the formula for working out the 'earth fault loop'? or can help with the ccc calcs or give any advice ,it wouold be much appreciated.
Anyone else going over on these dates???
Cheers Richard
Anyone know the formula for working out the 'earth fault loop'? or can help with the ccc calcs or give any advice ,it wouold be much appreciated.
Anyone else going over on these dates???
Cheers Richard
#2
Re: peer exam 25th &26th May
Zs = earth fault loop impedance
Uo = nominal phase voltage
Ia = current causing automatic operation
Zs = Uo/Ia
page 238 and 344 of the regs book
and check your answer on page 324 of the regs book.
hope this helps,
Del
Uo = nominal phase voltage
Ia = current causing automatic operation
Zs = Uo/Ia
page 238 and 344 of the regs book
and check your answer on page 324 of the regs book.
hope this helps,
Del
#3
Re: peer exam 25th &26th May
Thanks for the formula,
How would I work out the answer to Question 6 section 1 worksheet E of the peer workbook.
A 230v single phase sub-circuit is protected by a 20A type C circuit breaker.
what shall be the maximum loop impedance of the circuit(use the formula)
any takers?
cheers Richard
How would I work out the answer to Question 6 section 1 worksheet E of the peer workbook.
A 230v single phase sub-circuit is protected by a 20A type C circuit breaker.
what shall be the maximum loop impedance of the circuit(use the formula)
any takers?
cheers Richard
#5
Re: peer exam 25th &26th May
clause B4.5 page343-344 for the x 7.5
Table8 page 324
Page no might be different on latest rules book
Table8 page 324
Page no might be different on latest rules book
#6
Re: peer exam 25th &26th May
Ia = current causing automatic operation of the protective device
Ia for circuit-breakers is the mean tripping current as follows:
Type B = 4 × rated current
Type C = 7.5 × rated current
Type D = 12.5 × rated current
Ia for circuit-breakers is the mean tripping current as follows:
Type B = 4 × rated current
Type C = 7.5 × rated current
Type D = 12.5 × rated current
#7
Re: peer exam 25th &26th May
How many questions are in the work book? How long did it take to work through? How many hours a day did/do you spend on it?