Maximum demand, Please explain.

Maximum demand, Please explain.

Old Jun 22nd 2010, 7:07 am
  #31  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Foe Maxmium Demand Question No 3.

I was looking at the example on pg 360.

You have to put in 3 phase load and balance it ,the answer they looking for is the max current in the phase.
The trick is ensure try to balance the load as close as possiable,
I wiil attempt later,

let me know if you had worked out.
thanks.
Askar is offline  
Old Jun 22nd 2010, 7:37 am
  #32  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Askar
Foe Maxmium Demand Question No 3.

I was looking at the example on pg 360.

You have to put in 3 phase load and balance it ,the answer they looking for is the max current in the phase.
The trick is ensure try to balance the load as close as possiable,
I wiil attempt later,

let me know if you had worked out.
thanks.
I did try and balance it.
Jockstar is offline  
Old Jun 22nd 2010, 1:25 pm
  #33  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Determine the maximum demand of the heaviest loaded phase in a domesticv electrical instalation having the following load-

21 Lighting points 3 + 2 = 5A

28 10A single socket outlets
+
8 10A socket outlets = 10A + 5A = 15A

1 range(2 hotplates 6kW/230v =13.04A

6.8kW oven) 6800/230= 14.78A

1 air conditioner- (single phase 4.8kW) 4500/230 = 19.56 x 0.75= 14.67A

1 clothes dryer - ( single phase 4.8kW) see reg pg360 = 10.43A

1 washing machine - ( single phase self heating - 3.2kW) = 6.96A

1 3phase instantaneous water heater (5.3kW per phase) 5300/230 = 23 x 0.333= 7.67A per phase

1 3 phase motor rated at 7.5A per phase = 7.5A per phase



arrange into 3 phase

RED YELLOW BLUE

5A

10A 5A

13.04A 13.04A

14.78A


6.96A

10.43A

14.67A

7.67 7.67 7.67

7.5 7.5 7.5


Total


Red= 50.17 Yellow= 43.64 Blue= 44.62


Max demand red phase= 50.17A

I hope this is right,can some one check this please.
Askar is offline  
Old Jun 23rd 2010, 9:15 am
  #34  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

re balance red= 45.17 yellow = 48.64 blue = 44.62

total demand = yellow phase = 48.64A


is it right please any one
Askar is offline  
Old Jun 27th 2010, 8:05 am
  #35  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Hi Has any one done question No 3 on maximum demand.on peer work book

Re: Maximum demand, Please explain.

--------------------------------------------------------------------------------

re balance red= 45.17 yellow = 48.64 blue = 44.62

total demand = yellow phase = 48.64A


is it right please any one

Please reply.
Askar is offline  
Old Jul 5th 2010, 8:54 am
  #36  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Askar
Hi Has any one done question No 3 on maximum demand.on peer work book

Re: Maximum demand, Please explain.

--------------------------------------------------------------------------------

re balance red= 45.17 yellow = 48.64 blue = 44.62

total demand = yellow phase = 48.64A


is it right please any one

Please reply.
I got 69.03A , 42.84A and 43.82A
Jockstar is offline  
Old Jul 5th 2010, 8:57 am
  #37  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Question 4 i got 272.76A , 224.88A and 203.31A. Not sure if these are right. Views and opinions please.
Jockstar is offline  
Old Jul 5th 2010, 9:05 am
  #38  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

BTW the last calulation was worked out a while back. So it may be totally wrong.
Jockstar is offline  
Old Jul 7th 2010, 4:40 pm
  #39  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Q4 is not right,I think,please see example on pg361.
Askar is offline  
Old Aug 15th 2010, 10:33 am
  #40  
Just Joined
 
Joined: Jul 2010
Posts: 13
Andi1985 is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Originally Posted by Jockstar
Determine the maximum demand of a single phase 240V domestic installation.

28 Lighting points
+
8m Lighting track + 2 50W exhaust fans = 28+16+2= 46 points. Which is 3+2+2=7A

13 10A single socket outlets
+
9 10A double socket outlets + 1 1200 watts strip heaters = 13+9+1= 23 points so that would be 10+5=15A

2 50W exhaust fans

1 1200Watts strip heaters

1 14.5KW range 14500/240 = 60.41 x 0.5 = 30.2A

1 3.4kW storage H.W.S. 3400/240 = 14.16A

1 3.0kW clothes drier N/A



Total = 66.36A

This is what i get after revising the above. Just wondering where you get the extra 0.5A from?
Is this not total 72,9A?

If got
Ai)28p+16+2=46p= 7A
B)13p+18+1= 15A
C)30,2A+6,5A=36,7A
F) 14,2A
total: 72,9A
Andi1985 is offline  
Old Aug 16th 2010, 6:15 am
  #41  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Andi1985
Is this not total 72,9A?

If got
Ai)28p+16+2=46p= 7A
B)13p+18+1= 15A
C)30,2A+6,5A=36,7A
F) 14,2A
total: 72,9A
Nope. Have a look at mine and Askars
Jockstar is offline  
Old Aug 16th 2010, 8:20 am
  #42  
Just Joined
 
Joined: Jul 2010
Posts: 13
Andi1985 is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Originally Posted by Jockstar
Nope. Have a look at mine and Askars
And what is with the clothes drier? U both don´t calculate anything for this one, but it has an demand of 6.5A. It doesn´t count as laundry equipment? confused
Andi1985 is offline  
Old Aug 17th 2010, 12:52 pm
  #43  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Dont take cloth dryer.check the explaination on the max demand notes.
Askar is offline  
Old Aug 18th 2010, 7:36 am
  #44  
Just Joined
 
Joined: Jul 2010
Posts: 13
Andi1985 is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Hm...i still have the same.

Clothesdryer = Group C) Ranges, cooking appliances, laundry equipment or socket-outlets rated at more than 10A for the connection thereof

3000W:240V=12,5A x0,5=6,25A

Can´t find a note which say something else!!!
Andi1985 is offline  
Old Aug 19th 2010, 9:39 am
  #45  
Just Joined
 
Joined: Jul 2010
Posts: 13
Andi1985 is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Don´t know where i can edit my post, so double post.

Was at peer today, and u have to add the 6,25A from the clothes dryer to the max demand .
Andi1985 is offline  

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts