Maximum demand, Please explain.
Have been trying to work this out and as much as i can get most of it. Some things still confuse me. Ok from the PEER workbook Appendix C worsheet D.
Determine the maximum demand of a single domestic electrical installation supplied with single phase having the following load. 19 lighting points 6 10A double socket outets 16 single socket outlets 1 15A socket outlet 1 20A socket outlet 3 50W exaust fans 3 1000W strip heaters 12.4kW range 1 4.6kW instantaneous water heater 4 500W lights for tennis court Ok heres what i undertsand Load group A(i) 19 lighting points= 3A 3X 50W exaust fans = 135? points going from an example in the regs So 3+2+2+2=9? Load group A(ii) 500W lights = non applicable? Load group B(i) 6 double sockets+16 single sockets =22points? 3 x 1000W strip heaters = 3points(using another example in the book ie 1point for one 1000W heater.) where is this info? Load group B(ii) 1 x 15A socket outlet = 10A? Load group B(iii) 1 x 20A socket outlet = 15A? Load group C 12.4kW range = _____ x 05=______Where do i get this info? Load group F - water heater 4.6W = ____A? I hope this makes sense to someone. Help please. |
Re: Maximum demand, Please explain.
Originally Posted by Jockstar
(Post 8631365)
Have been trying to work this out and as much as i can get most of it. Some things still confuse me. Ok from the PEER workbook Appendix C worsheet D.
Determine the maximum demand of a single domestic electrical installation supplied with single phase having the following load. 19 lighting points 6 10A double socket outets 16 single socket outlets 1 15A socket outlet 1 20A socket outlet 3 50W exaust fans 3 1000W strip heaters 12.4kW range 1 4.6kW instantaneous water heater 4 500W lights for tennis court Ok heres what i undertsand Load group A(i) 19 lighting points= 3A correct +2A for fans =5A 3X 50W exaust fans = 135? points going from an example in the regs So 3+2+2+2=9?read footnote c in notes to table c1-add to lights Load group A(ii) 500W lights = non applicable? .75% OF CONNECTED LOad 6.25A Load group B(i) 6 double sockets+16 single sockets =22points? 3 x 1000W strip heaters = 3points(using another example in the book ie 1point for one 1000W heater.) where is this info? FOOTNOTE(i)lees than 10A add to B Load group B(ii) 1 x 15A socket outlet = 10A?}footnote (J) Load group B(iii) 1 x 20A socket outlet = 15A? Load group C 12.4kW range = _____ x 05=______Where do i get this info? 12400/230 =53.9A 54A x 50% 27A Load group F - water heater 4.6W = ____A? 4600/230 x 33.3%= 6.66A I hope this makes sense to someone. Help please. |
Re: Maximum demand, Please explain.
Originally Posted by Lee and Joanne
(Post 8631861)
does this make sense
Please clarify where did you get 2amps for fan. I assume that 19 lights plus 3 x 50w fan total 22 lights = 3A + 2A. is this correct. please give a feed back will be appreciated. thanks |
Re: Maximum demand, Please explain.
:fingerscrossed:
Originally Posted by Askar
(Post 8632246)
Hi ,
Please clarify where did you get 2amps for fan. I assume that 19 lights plus 3 x 50w fan total 22 lights = 3A + 2A. is this correct. please give a feed back will be appreciated. thanks |
Re: Maximum demand, Please explain.
yes that is correct
|
Re: Maximum demand, Please explain.
Can neone plz tell that how many questions in total comes in wiring rule exam in peer
|
Re: Maximum demand, Please explain.
Thanks mate.:thumbup:
|
Re: Maximum demand, Please explain.
Originally Posted by Lee and Joanne
(Post 8631861)
does this make sense
Load group A(ii) 500W lights = non applicable? .75% OF CONNECTED LOad 6.25A |
Re: Maximum demand, Please explain.
Its 4 X 500w = 2000/230 x .75 = 6.25.
hope that explains. |
Re: Maximum demand, Please explain.
Originally Posted by Jockstar
(Post 8631365)
Have been trying to work this out and as much as i can get most of it. Some things still confuse me. Ok from the PEER workbook Appendix C worsheet D.
Determine the maximum demand of a single domestic electrical installation supplied with single phase having the following load. 19 lighting points 6 10A double socket outets 16 single socket outlets 1 15A socket outlet 1 20A socket outlet 3 50W exaust fans 3 1000W strip heaters 12.4kW range 1 4.6kW instantaneous water heater 4 500W lights for tennis court Ok heres what i undertsand Load group A(i) 19 lighting points= 3A 3X 50W exaust fans = 2A total 3+2 = 5A Load group A(ii) 500W lights = Still not sure how you get that. Load group B(i) 6 double sockets+16 single sockets =22points? 3 x 1000W strip heaters = 3points= 22+3=25points so 10A+5A=15A? Load group B(ii) 1 x 15A socket outlet = 10A Load group B(iii) 1 x 20A socket outlet = 15A + base loading of 15A= 40A? Load group C 12.4kW range = 12400/230= 53.9(54) 54x 0.5= 27A Load group E - water heater 4.6W = 4600/230= 20A x 0.33= 6.66A I hope this makes sense to someone. Help please. |
Re: Maximum demand, Please explain.
Originally Posted by Askar
(Post 8638229)
Its 4 X 500w = 2000/230 x .75 = 6.25.
hope that explains. |
Re: Maximum demand, Please explain.
Originally Posted by Jockstar
(Post 8638247)
Ah! Ok. I forgot it was times 4. lol Does the rest look right?
3X 50W exaust fans = 2A total 3+2 = 5A Load group A(ii) 500W lights = 4 x 500W = 2000W/230 x 0.75 = 6.5A Load group B(i) 6 double sockets+16 single sockets =22points? 3 x 1000W strip heaters = 3points= 22+3=25points so 10A+5A=15A? Load group B(ii) 1 x 15A socket outlet = 10A Load group B(iii) 1 x 20A socket outlet = 15A + base loading of 15A= 40A? Load group C 12.4kW range = 12400/230= 53.9(54) 54x 0.5= 27A Load group E - water heater 4.6W = 4600/230= 20A x 0.33= 6.66A So overall total would be 100A? |
Re: Maximum demand, Please explain.
The rest is right except, Group B(iii) is 1x 20 amps socket = 15amps
Total demand is about 85.15amps. |
Re: Maximum demand, Please explain.
Originally Posted by Askar
(Post 8638358)
The rest is right except, Group B(iii) is 1x 20 amps socket = 15amps
Total demand is about 85.15amps. |
Re: Maximum demand, Please explain.
The correct answer is 95.16 amps
|