Re: Maximum demand, Please explain.
Foe Maxmium Demand Question No 3.
I was looking at the example on pg 360. You have to put in 3 phase load and balance it ,the answer they looking for is the max current in the phase. The trick is ensure try to balance the load as close as possiable, I wiil attempt later, let me know if you had worked out. thanks. |
Re: Maximum demand, Please explain.
Originally Posted by Askar
(Post 8648003)
Foe Maxmium Demand Question No 3.
I was looking at the example on pg 360. You have to put in 3 phase load and balance it ,the answer they looking for is the max current in the phase. The trick is ensure try to balance the load as close as possiable, I wiil attempt later, let me know if you had worked out. thanks. |
Re: Maximum demand, Please explain.
Determine the maximum demand of the heaviest loaded phase in a domesticv electrical instalation having the following load-
21 Lighting points 3 + 2 = 5A 28 10A single socket outlets + 8 10A socket outlets = 10A + 5A = 15A 1 range(2 hotplates 6kW/230v =13.04A 6.8kW oven) 6800/230= 14.78A 1 air conditioner- (single phase 4.8kW) 4500/230 = 19.56 x 0.75= 14.67A 1 clothes dryer - ( single phase 4.8kW) see reg pg360 = 10.43A 1 washing machine - ( single phase self heating - 3.2kW) = 6.96A 1 3phase instantaneous water heater (5.3kW per phase) 5300/230 = 23 x 0.333= 7.67A per phase 1 3 phase motor rated at 7.5A per phase = 7.5A per phase arrange into 3 phase RED YELLOW BLUE 5A 10A 5A 13.04A 13.04A 14.78A 6.96A 10.43A 14.67A 7.67 7.67 7.67 7.5 7.5 7.5 Total Red= 50.17 Yellow= 43.64 Blue= 44.62 Max demand red phase= 50.17A I hope this is right,can some one check this please.:fingerscrossed: |
Re: Maximum demand, Please explain.
re balance red= 45.17 yellow = 48.64 blue = 44.62
total demand = yellow phase = 48.64A is it right please any one |
Re: Maximum demand, Please explain.
Hi Has any one done question No 3 on maximum demand.on peer work book
Re: Maximum demand, Please explain. -------------------------------------------------------------------------------- re balance red= 45.17 yellow = 48.64 blue = 44.62 total demand = yellow phase = 48.64A is it right please any one Please reply.:fingerscrossed: |
Re: Maximum demand, Please explain.
Originally Posted by Askar
(Post 8660078)
Hi Has any one done question No 3 on maximum demand.on peer work book
Re: Maximum demand, Please explain. -------------------------------------------------------------------------------- re balance red= 45.17 yellow = 48.64 blue = 44.62 total demand = yellow phase = 48.64A is it right please any one Please reply.:fingerscrossed: |
Re: Maximum demand, Please explain.
Question 4 i got 272.76A , 224.88A and 203.31A. Not sure if these are right. Views and opinions please.
|
Re: Maximum demand, Please explain.
BTW the last calulation was worked out a while back. So it may be totally wrong.
|
Re: Maximum demand, Please explain.
Q4 is not right,I think,please see example on pg361.
|
Re: Maximum demand, Please explain.
Originally Posted by Jockstar
(Post 8647926)
Determine the maximum demand of a single phase 240V domestic installation.
28 Lighting points + 8m Lighting track + 2 50W exhaust fans = 28+16+2= 46 points. Which is 3+2+2=7A 13 10A single socket outlets + 9 10A double socket outlets + 1 1200 watts strip heaters = 13+9+1= 23 points so that would be 10+5=15A 2 50W exhaust fans 1 1200Watts strip heaters 1 14.5KW range 14500/240 = 60.41 x 0.5 = 30.2A 1 3.4kW storage H.W.S. 3400/240 = 14.16A 1 3.0kW clothes drier N/A Total = 66.36A This is what i get after revising the above. Just wondering where you get the extra 0.5A from? If got Ai)28p+16+2=46p= 7A B)13p+18+1= 15A C)30,2A+6,5A=36,7A F) 14,2A total: 72,9A |
Re: Maximum demand, Please explain.
Originally Posted by Andi1985
(Post 8778379)
Is this not total 72,9A?
If got Ai)28p+16+2=46p= 7A B)13p+18+1= 15A C)30,2A+6,5A=36,7A F) 14,2A total: 72,9A |
Re: Maximum demand, Please explain.
Originally Posted by Jockstar
(Post 8779960)
Nope. Have a look at mine and Askars
|
Re: Maximum demand, Please explain.
Dont take cloth dryer.check the explaination on the max demand notes.
|
Re: Maximum demand, Please explain.
Hm...i still have the same.
Clothesdryer = Group C) Ranges, cooking appliances, laundry equipment or socket-outlets rated at more than 10A for the connection thereof 3000W:240V=12,5A x0,5=6,25A Can´t find a note which say something else!!! |
Re: Maximum demand, Please explain.
Don´t know where i can edit my post, so double post.
Was at peer today, and u have to add the 6,25A from the clothes dryer to the max demand ;). |