Hot Water Systems
Advice please, do Spanish plumbing systems normally have the hot water tank directly fed from the main?
Problem we are having is the tank is venting when the water gets hot which wouldnt happen in the Uk where there would be a tank reducing the pressure from the main. Are there any circuit diagrams online showing how these systems are normally plumbed ? thanks |
Re: Hot Water Systems
Originally Posted by Domino
(Post 9746555)
Advice please, do Spanish plumbing systems normally have the hot water tank directly fed from the main?
Problem we are having is the tank is venting when the water gets hot which wouldnt happen in the Uk where there would be a tank reducing the pressure from the main. Are there any circuit diagrams online showing how these systems are normally plumbed ? thanks http://www.google.es/search?q=hot+wa...w=1024&bih=497 |
Re: Hot Water Systems
in the Uk where there would be a tank reducing the pressure from the main FYI: http://www.boilerguide.co.uk/article...eating-systems |
Re: Hot Water Systems
Originally Posted by anonimouse
(Post 9746643)
the landlord says they don't fit timers on it either, so its either on or off dependent on whether or not we go down to the basement to switch on\off won't be able to see it for a couple ofweeks but its driving the BH nuts at the moment. rgds |
Re: Hot Water Systems
Originally Posted by missile
(Post 9746661)
Must be a while since you lived in the UK?:nod:
FYI: http://www.boilerguide.co.uk/article...eating-systems I note that both the systems shown in your reference are for central heating not for hot water system but both have a tank......... |
Re: Hot Water Systems
Our electric heated tank is feed from the mains (as most are here), when it reaches a set temperature it stops heating and will remain static until the temperature falls, or you demand water, when the cycle starts again.
No drips/leaks etc and there should not be any either (to my mind) unless the internal thermostat becomes faulty when I guess it will heat the water so much it reaches boiling point and will attempt to exit as yours is doing. Or you simply have a leak. ;) |
Re: Hot Water Systems
Originally Posted by Domino
(Post 9746720)
i am in the uk as I type, and we have a tank tween the mains and the hot water cylinder. Which is fairly standard.
I note that both the systems shown in your reference are for central heating not for hot water system but both have a tank......... â– A combi boiler heats water on demand requiring no tanks â– High pressure systems These systems supply mains pressure hot water â– Conentional Gravity Fed systems often comes from a feed tank or expansion tank In the UK (and spain) modern systems are fed from the mains. Only the older gravity fed heating systems require a storage tank. |
Re: Hot Water Systems
Turn the thermostat down and see if it shuts down, perhaps it needs replacing.
Also you could buy a timer plugin and put between the supply and the water heater. |
Re: Hot Water Systems
Thanks for the responses, this is the first time we have encountered a direct system - despite the protestations, there are millions of in-direct systems in the UK and they are all we have ever encountered.
Remember, I am in uk and BH is Spain where the system is, so at the moment I am trying to solve a problem I cannot see and touch. it is a new house, new system and the landlord left the system on max temp. It has been turned down twice and still overflows (vents). BH asked landlord to fit a timer but he said "No, thats not what we do". One thing I have noted is that the UK requires regular checks of these pressurised systems - is that the same in the UK or is it a thing no one worries about ? |
Re: Hot Water Systems
Originally Posted by Domino
(Post 9747561)
Thanks for the responses, this is the first time we have encountered a direct system - despite the protestations, there are millions of in-direct systems in the UK and they are all we have ever encountered.
Remember, I am in uk and BH is Spain where the system is, so at the moment I am trying to solve a problem I cannot see and touch. it is a new house, new system and the landlord left the system on max temp. It has been turned down twice and still overflows (vents). BH asked landlord to fit a timer but he said "No, thats not what we do". One thing I have noted is that the UK requires regular checks of these pressurised systems - is that the same in the UK or is it a thing no one worries about ? The concept of 'Health and Safety' doesn't really seem to exist in Spain. They make feeble attempts at it, but when push comes to shove, it gets ignored! |
Re: Hot Water Systems
Originally Posted by snikpoh
(Post 9747635)
The concept of 'Health and Safety' doesn't really seem to exist in Spain.
They make feeble attempts at it, but when push comes to shove, it gets ignored! European Agency for Safety and Health at Work Gran Via 33 E-48009 Bilbao, Spain Tel: + 34 944-794-360 Fax: + 34 944-794-383 Web: http://osha.europa.eu |
Re: Hot Water Systems
A bit off the subject but in the same vein. I need to replace my outdoor gas water heater and have found a few advertised and offering different size/capacity of 5ltr / 10ltr as Iam not in Spain until the weekend anyone any idea what capacity I should be looking for. 3 Bedrooms, 2 Bathrooms, Kitchen, Living room, Dinning room. Thanks Stuart.
|
Re: Hot Water Systems
Originally Posted by stuart from barnsley
(Post 9747889)
A bit off the subject but in the same vein. I need to replace my outdoor gas water heater and have found a few advertised and offering different size/capacity of 5ltr / 10ltr as Iam not in Spain until the weekend anyone any idea what capacity I should be looking for. 3 Bedrooms, 2 Bathrooms, Kitchen, Living room, Dinning room. Thanks Stuart.
a 10l may not fit in the gap of a 5l ... :eek: even getting someone (?) to take the physical measurements would help you rgds |
Re: Hot Water Systems
Will do, but their is plenty of space around the original one.
|
Re: Hot Water Systems
Originally Posted by stuart from barnsley
(Post 9748469)
Will do, but their is plenty of space around the original one.
|
Re: Hot Water Systems
Don`t forget electronic ignition as it`s outside. ;);)
|
Re: Hot Water Systems
The two most common types of boiler here are gas and electric,
The gas type turn on and heat the water only when you open a tap , the most common flow rate is 11 litres per min. Electric cylinders, heat and store water to a pre set temperature, and that is controlled by a thermostat, if the thermostat is not working and is not turning the heater element off the water will boil and vent from the safety valve on the cold water inlet. As some one else said maybe you could fit a timer, to limit the daily heating. |
Re: Hot Water Systems
Originally Posted by stuart from barnsley
(Post 9747889)
A bit off the subject but in the same vein. I need to replace my outdoor gas water heater and have found a few advertised and offering different size/capacity of 5ltr / 10ltr as Iam not in Spain until the weekend anyone any idea what capacity I should be looking for. 3 Bedrooms, 2 Bathrooms, Kitchen, Living room, Dinning room. Thanks Stuart.
|
Re: Hot Water Systems
I have an electric water heater which is in the bedroom. When we moved in the whole water system was fed from tank on terrace gravity and pressure was rubbish had to chase around for a shower to get wet although the mains pressure into the house is quite high. I was advised how to put a loop in by someone which allows mains pressure but also in case of failure of mains water supply then you have back up of storage tank on terrace. I was advised and did put a pressure reduction valve in the supply pipe where it enters the house set to around 3 bar and the whole system works fine. As I don't seem to be able to regulate the thermostat on water heater I have it plugged into a simple plug in timer and set it to come on early morning and late afternoon which is fine for us obviously can override timer if hot water runs out. Don't know if this saves much electric versus having water heater on all the time? All in all the system I have been using now 3 years without any complaints good pressure for shower and not that difficult to do yourself.
|
Re: Hot Water Systems
Originally Posted by bobd22
(Post 9754884)
... a simple plug in timer and set it to come on early morning and late afternoon which is fine for us obviously can override timer if hot water runs out. Don't know if this saves much electric versus having water heater on all the time?...
|
Re: Hot Water Systems
Hi Jimenato,
300 per month !!! it is worth considering pre heating the water via a solar water heater before enters the electric boilers, you will save a fortune !!! Tony |
Re: Hot Water Systems
at €300 sounds like very large amount of water there, not being thermally insulated.
I hate to say it but some of the old UK ideas come to mind, smaller tanks (do you need 100L + for the household (?) and thermally insulated, after all do you need it for 12m (?) would suggest a timer schedule for all day only or 3-4hrs each morn and nite. but you know your needs better than me or anyone else here rgds |
Re: Hot Water Systems
Originally Posted by jimenato
(Post 9758038)
Would it be better to turn them on an hour before we need to use them?
If you find that you don't have enough hot water later in the day then just set another hour on the timer for late afternoon. Unless you have a 100% insulated tank keeping water hot when you don't need it wastes energy. |
Re: Hot Water Systems
Originally Posted by Fred James
(Post 9758172)
Put a timer on them set to run for 3 hours before you need the water in the morning. Also set the thermostat to a lower temperature. This could save you at least 50% of the cost compared to leaving it on all the time.
If you find that you don't have enough hot water later in the day then just set another hour on the timer for late afternoon. Unless you have a 100% insulated tank keeping water hot when you don't need it wastes energy. |
Re: Hot Water Systems
Originally Posted by bobd22
(Post 9754884)
I have an electric water heater which is in the bedroom. When we moved in the whole water system was fed from tank on terrace gravity and pressure was rubbish had to chase around for a shower to get wet although the mains pressure into the house is quite high. I was advised how to put a loop in by someone which allows mains pressure but also in case of failure of mains water supply then you have back up of storage tank on terrace. I was advised and did put a pressure reduction valve in the supply pipe where it enters the house set to around 3 bar and the whole system works fine. As I don't seem to be able to regulate the thermostat on water heater I have it plugged into a simple plug in timer and set it to come on early morning and late afternoon which is fine for us obviously can override timer if hot water runs out. Don't know if this saves much electric versus having water heater on all the time? All in all the system I have been using now 3 years without any complaints good pressure for shower and not that difficult to do yourself.
|
Re: Hot Water Systems
A lot of the new electric boilers do NOT have thermostats that the user can adjust - they are pre-set. They are also pre-insulated and so can be mounted outside without the need for additional insulation.
We have a 300l boiler which is on all the time, is mounted outside and is EXTREMELY efficient. We used to have the gas (on-demand) type but we (well my wife mainly) got increasingly fed up with the gas running out half way through a shower! Also, it used to take ages for the hot water to get from the boiler to the various bathrooms. We considered installing other gas boilers nearer the bathrooms but were persuaded to go electric due to their improved efficiency. The shower pressure is, of course, mains pressure which is akin to a power shower:thumbup: |
Re: Hot Water Systems
Originally Posted by tony
(Post 9758095)
Hi Jimenato,
300 per month !!! it is worth considering pre heating the water via a solar water heater before enters the electric boilers, you will save a fortune !!! Tony I might consider solar water heating but ours are rented premises. Incidentally our rubbish collection and water bill is over 500 Euros every three months - the vast bulk of which is for rubbish - which I take myself to the punto limpio.:frown: |
Re: Hot Water Systems
Originally Posted by jimenato
(Post 9762185)
I should point out that it's not only water heating. We have two very large freezers and five commercial fridges.
I might consider solar water heating but ours are rented premises. Incidentally our rubbish collection and water bill is over 500 Euros every three months - the vast bulk of which is for rubbish - which I take myself to the punto limpio.:frown: see, all these "hidden" costs that people do not take in to account when they want to come and "live the dream" playing "mine host" to all the touristico's looking for roast beef, tatties, yorkshires and gravy. |
Re: Hot Water Systems
Originally Posted by jimenato
(Post 9762185)
I should point out that it's not only water heating.
Incidentally our rubbish collection and water bill is over 500 Euros every three months - the vast bulk of which is for rubbish - which I take myself to the punto limpio.:frown: Another, more petty example which I think illustrates the point is at the ajuntamento (here, anyway), when they need a copy of some document (e.g., your passport), they refuse to use the copy machine that's sitting over in the corner. No, you have to find a local copy shop and pay €1 to copy your passport, and return and stand in the queue again. Seems to me that they would WANT to make the copy themselves. Otherwise you could easily forge the copy. But I suppose it saves a cent or two. But then again... similar logic seems to be the basis for everything - the locals around here will spend a fortune digging a drainage system into their floor to drain the water from their house when it rains, while completely ignoring the hole in the roof. |
Re: Hot Water Systems
I want to install an unvented indirect hot water cylinder, with the water being heated from a back boiler on a wood burning stove (imported from UK). These cylinders cost £500 to £1000 in UK, but I can't find on any Spanish web pages. Any ideas if they can be obtained in Spain? - including a decent translation of "unvented indirect hot water cylinder". thanks
|
Re: Hot Water Systems
Originally Posted by BristolGirona
(Post 9798744)
I want to install an unvented indirect hot water cylinder, with the water being heated from a back boiler on a wood burning stove (imported from UK). These cylinders cost £500 to £1000 in UK, but I can't find on any Spanish web pages. Any ideas if they can be obtained in Spain? - including a decent translation of "unvented indirect hot water cylinder". thanks
BE is a very large expat website, so if you have problems finding your way around we have concierges who will try to direct you. The moderators for the Spanish forums are Mitzyboy and Fred James, moderators are there to ensure that the site runs smoothly within the rules of BE. Problems and complaints should always be addressed to a moderador who will look into the matter and deal with it efficiently and fairly. Our members who post in the Spain Forums are friendly and helpful with a wealth of knowledge of the issues of living in Spain. At the top of the page you will find a quirkily named thread called Free Beer which is full of important and useful information. Hope you enjoy your time participating in the forums. Please let me know if you need any further help. Rosemary |
Re: Hot Water Systems
Originally Posted by BristolGirona
(Post 9798744)
I want to install an unvented indirect hot water cylinder, with the water being heated from a back boiler on a wood burning stove (imported from UK). These cylinders cost £500 to £1000 in UK, but I can't find on any Spanish web pages. Any ideas if they can be obtained in Spain? - including a decent translation of "unvented indirect hot water cylinder". thanks
|
Re: Hot Water Systems
Originally Posted by BristolGirona
(Post 9798744)
I want to install an unvented indirect hot water cylinder, with the water being heated from a back boiler on a wood burning stove (imported from UK). These cylinders cost £500 to £1000 in UK, but I can't find on any Spanish web pages. Any ideas if they can be obtained in Spain? - including a decent translation of "unvented indirect hot water cylinder". thanks
http://tecnihogar.es/blog/2011/09/26...co-termat-50l/ http://www.solarsunlite.com/installation_drawings.php show how to do it physically and they are in spain That was found using the english words on google.es, search for pages in spain. for some translations try http://www.wordreference.com/es/tran...ranword=heater hope this helps |