peer CCC Calcs
#1
hi all,
Im off to Adelaide next week and still not quiet sure about the ccc calcs.
Q 6 pg 71 Question asks
A three phase 415v circuit is to supply a load of 75A.It is intended to use V-75 4 core plus earth (round) insulated and sheathed cables,bunched together with other equivalent circuits in air.
The circuit is to operate in an environment with ambient temp of 55 degrees,route lenght from supply to load is 35 metres,conductor temp 75c
Calculate and determine the minmum conductor size required?
and
what is the volt drop from the supply to the load,does this comply with the permissable voltdrop as per az/nzs3000?
I made it from table 12 35mm
and vd of 3.88v
max permissable= 5v
am i correct with these or do i need to add a derating factor for ambient temp
any help would be appreciated
many thanks Richard
Im off to Adelaide next week and still not quiet sure about the ccc calcs.
Q 6 pg 71 Question asks
A three phase 415v circuit is to supply a load of 75A.It is intended to use V-75 4 core plus earth (round) insulated and sheathed cables,bunched together with other equivalent circuits in air.
The circuit is to operate in an environment with ambient temp of 55 degrees,route lenght from supply to load is 35 metres,conductor temp 75c
Calculate and determine the minmum conductor size required?
and
what is the volt drop from the supply to the load,does this comply with the permissable voltdrop as per az/nzs3000?
I made it from table 12 35mm
and vd of 3.88v
max permissable= 5v
am i correct with these or do i need to add a derating factor for ambient temp
any help would be appreciated
many thanks Richard
#3
so from table 22(3x circuits bunched in air)
derating factor is 0.75
table 27 (ambient temp 55c)
derating factor is 0.72
So the calc is 75(A) x 1/0.75x1/0.72= 75x1.33x1.38=137(A)
Table 12= 137A = 70mm cable
on the vd do I use the original 75A or the 137A ?
Is this the correct calc im using?
Cheers Richard
derating factor is 0.75
table 27 (ambient temp 55c)
derating factor is 0.72
So the calc is 75(A) x 1/0.75x1/0.72= 75x1.33x1.38=137(A)
Table 12= 137A = 70mm cable
on the vd do I use the original 75A or the 137A ?
Is this the correct calc im using?
Cheers Richard
#5
so using table 12 137A =70mm cable
table 42= 70mm at 75c =a factor of 0.583
vd = mV/Am x length x Current=0.583 x 35(m) x 75(A) /1000
= 1.53volts
is this correct?
many thanks Richard
table 42= 70mm at 75c =a factor of 0.583
vd = mV/Am x length x Current=0.583 x 35(m) x 75(A) /1000
= 1.53volts
is this correct?
many thanks Richard
#7
Just Joined
Joined: Sep 2009
Posts: 12

Thanks for your helpful postings...
In your info:
Table 12= 137A = 70mm cable
(How you have found this 70mm from 137am? Can you please tell me?