somme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to behold
Question Calculation Help Please

Hi Guys, OH taking his peers course exam next week and the following question has him doughting himself and losing sleep if you could help please.

A three phase circuit is to supply a load of 75amps. It is intended to use V-75 3 half plus earth (round) insulated and sheathed cables, bunched together with other two equivalent circuits in air.

The circuit is to operate in an enviroment with ambient tempreture of 55 degrees. Route length from supply to load is 35 meters, conductor temp 60 deg.c

Calculate and determine the minimum conductor size required.
What is the voltage drop from the supply to the load? Does this comply with the permissible voltage drop as per As/NZS 3000:2000?

He is getting 70mm but does not think this is right and does not know where he is going wrong

Any help would be really appreciated
somme is offline  
Old Jun 17th 2008, 3:32 am
  #2  
BE Forum Addict
Thread Starter
 
somme's Avatar
 
Joined: Mar 2007
Location: Peregian Beach SC Qld
Posts: 1,522
somme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to beholdsomme is a splendid one to behold
Default Re: Calculation Help Please

Thanks for your help guys
somme is offline  
Old Jun 20th 2008, 11:05 am
  #3  
Just Joined
 
Joined: May 2008
Posts: 11
geordie2008 is an unknown quantity at this point
Default Re: Calculation Help Please

35 sq mm,
table 22, derating factor 0.75 for bunched together with other two circuit, 75/0.75=100A,
table 12, 35sq mm.

voltage drop , table 42, 1.06mV/A.m,1.06*75*35=2782.5 mv.
geordie2008 is offline  

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Contact Us - Archive - Advertising - Cookie Policy - Privacy Statement - Terms of Service -

Copyright © 2024 MH Sub I, LLC dba Internet Brands. All rights reserved. Use of this site indicates your consent to the Terms of Use.