step up/down transformer
hi everyone, I am moving to Newfoundland in November. Apart from a couple of items which are dual voltage, I am leaving my electrical stuff behind. However I am considering bringing my sewing machine- for occasional use only. I have been reading around step up/down transformers etc. My machine is 220-240 voltage, 50 Hz and 50 W.
I understand the bit about changing from 220-240 to 110, and think I will need a 100 Watt transformer, but I'm a bit confused about the 50 Hz bit! Basically has anyone brought a sewing machine from the Uk and successfully used it in Canada? Also do I need to buy the transformer in Canada, or here in the UK and put it in the container which is heading off in 2 weeks. Any advice would be much appreciated kind regards Shirley |
Re: step up/down transformer
50Hz sewing maching should be OK with a 110-220v Transformer.
Purchase one when you get here In the following thread http://britishexpats.com/forum/canad...ooster-881051/ |
Re: step up/down transformer
North American mains is 60Hz, so depending on the motor, it might not run at the right speed.
|
Re: step up/down transformer
I bought my Transformer in Canada from Amazon, It was $100 and took less than a week to arrive, it is about the size of a shoe box. I have more than returned the outlay, as my Dyson Vacuum works in Canada and they cost a small fortune to buy new here.
The thread that not2old pointed out is my thread about just this matter. |
Re: step up/down transformer
hi guys thanks for the very helpful information, and links in referenced thread. It can be bewildering when trying to weigh up the cost of replacing items while trying to ensure I don't blow up our home in Canada. We are heading over for a familiarisation visit in 2-3 weeks to get practical stuff organised, in advance of our final move, so i'm sure I will be back with more questions!
|
Re: step up/down transformer
I have a transformer sitting unused right now. Used it for some hi-fi gear and other stuff that wouldn't run here.
Yours if you want it. (I'm in St. John's) WeeGem |
Re: step up/down transformer
Originally Posted by ShirleyEB
(Post 12058292)
hi guys thanks for the very helpful information, and links in referenced thread. It can be bewildering when trying to weigh up the cost of replacing items while trying to ensure I don't blow up our home in Canada. We are heading over for a familiarisation visit in 2-3 weeks to get practical stuff organised, in advance of our final move, so i'm sure I will be back with more questions!
|
Re: step up/down transformer
Originally Posted by WeeGem
(Post 12058371)
I have a transformer sitting unused right now. Used it for some hi-fi gear and other stuff that wouldn't run here.
Yours if you want it. (I'm in St. John's) WeeGem |
Re: step up/down transformer
Originally Posted by Oakvillian
(Post 12058484)
But since a sewing machine has a variable speed motor controlled by the foot pedal, you'll be able to run it at the required speed by being a bit lighter on the pedal - and when you're stitching a long straight seam the flat-out speed will feed the fabric through a little bit quicker! We have a UK sewing machine that gets plugged in through a transformer and it has worked perfectly well for a decade.
|
Re: step up/down transformer
Originally Posted by Yorkiechef
(Post 12058249)
I bought my Transformer in Canada from Amazon, It was $100 and took less than a week to arrive, it is about the size of a shoe box. I have more than returned the outlay, as my Dyson Vacuum works in Canada and they cost a small fortune to buy new here.
The thread that not2old pointed out is my thread about just this matter. |
Re: step up/down transformer
thanks jukebox widow- useful to know that my machine will be viable. It's good we can take these things rather than paying a fortune for replacement!!
|
Re: step up/down transformer
I don't respond on here much but I wasn't leaving the UK without my 3 sewing machines. The sewing machine store sold me the the step-up step-down transformer and it's worked fine for me for the past 12 years. Having a sewing business I use them all the time.
|
Re: step up/down transformer
It will run fine. You may find it runs either a little faster or a little slower (if the synchronous speed is exceeded). In all likelihood it won't be that noticeable.
The only thing you need to be careful with due to the change in frequency is either sensitive electronic devices or larger motors greater than around 3kW. |
Re: step up/down transformer
Originally Posted by Markicof
(Post 12064995)
..... The only thing you need to be careful with due to the change in frequency is either sensitive electronic devices or larger motors greater than around 3kW.
|
Re: step up/down transformer
Originally Posted by Markicof
(Post 12064995)
It will run fine. You may find it runs either a little faster or a little slower (if the synchronous speed is exceeded). In all likelihood it won't be that noticeable.
The only thing you need to be careful with due to the change in frequency is either sensitive electronic devices or larger motors greater than around 3kW. Looked on line at the UK Argos catalog store in the UK & indeed they sell 3Kw (3000watts) electric kettles for domestic household use. Breville was the one brand that is 3000 watts. Now I know why my sisters kettle boils water so fast In the UK, take the 3Kw/240Volts, is approx 12.5amps, which is pushing the upper limit of a conventional 13 amp house socket Looked & could not find any sewing machines rated at 3000 watts - something lon average 100watts, with load, I'm guessing ~300watts. Mind you the price of some of the fancy computerized sewing machines range £2000 - £6000 in price For the OP, you may want to check the power rating of your machines to make sure they wont exceed the approx 1800 watts Pulaski posted on above, also that if they are computerized you may want to check with the manufacturer to see if the software will work without issues or will there be any issues for any reason over this side of the pond As well as if service & parts for your machines is available here in Canada . |
Re: step up/down transformer
Originally Posted by ShirleyEB
(Post 12058677)
hi Wee Gem that's very much appreciated, and nice to 'meet' another expat when I move to St John's. I'm moving over mid November and would be happy to try yours out
|
Re: step up/down transformer
Thanks very much everyone for your help
|
Re: step up/down transformer
Just buy a transformer. Believe me, almost EVERYTHING will work. For some things, maybe the Hz thingy might be a bit different, but unless you're running some sort of life enhancing gizmo, in my experience it really doesn't matter.
|
Re: step up/down transformer
Hi Shirley,
My Family and I plan to move to Ontario in the New Year. We are also from Northern Ireland. Perhaps we could share our experiences to date as it is a very daunting process. The chat would be interesting if nothing else. Thanks Farmboy |
Re: step up/down transformer
Originally Posted by Farmboy1892
(Post 12072169)
Hi Shirley,
My Family and I plan to move to Ontario in the New Year. We are also from Northern Ireland. Perhaps we could share our experiences to date as it is a very daunting process. The chat would be interesting if nothing else. Thanks Farmboy Shirley |
Re: step up/down transformer
Honestly transformers are such a faff you're better off buying new stuff imx. I've got a whole shelf full of those transformers for things I brought over from the UK and hardly use, e.g. paper shredder. I use them with drills as well and yes they do rotate at a different speed, not exactly a big problem though, just use a different setting.
|
Re: step up/down transformer
As a kettle is just a fixed resistive element (R) it willwork in Canada , it’ll just take a little longer to boil as the current will belower due to the lower voltage
If any care to post up the resistance of a Canadian kettle,I’m quite will to take a measurement of one here, I’m betting there’s not much difference Interestingly I used an Old Dyson DC02, for an experimentyears ago I ran it on just 120v/60hz andit still out performed a traditional bag type cleaner J |
Re: step up/down transformer
I had an interesting chat with my house inspector about the voltages. This is all subject to further research and confirmation:
He explained that voltages are 240V coming to the house in two live lines, and that only one live line is generally used inside the house. There are two common exceptions, electric cookers/ranges and driers which run on the full 240V! So in theory, a qualified electrician should have no trouble running additional 240V sockets with full British sockets. However, thinking about it more, there is a difference in frequency, 60Hz over 50Hz, so something won't be happy I bet! |
Re: step up/down transformer
Originally Posted by weves
(Post 12074126)
I had an interesting chat with my house inspector about the voltages. This is all subject to further research and confirmation:
He explained that voltages are 240V coming to the house in two live lines, and that only one live line is generally used inside the house. There are two common exceptions, electric cookers/ranges and driers which run on the full 240V! So in theory, a qualified electrician should have no trouble running additional 240V sockets with full British sockets. However, thinking about it more, there is a difference in frequency, 60Hz over 50Hz, so something won't be happy I bet! The wiring for a 240v socket in North America though is quite unlike 240v wiring in the UK because in the UK all 240v is in one wire, whereas in North America you need two wires each of 120v to get a 240v socket. ..... So you (ideally) need four wires - two lives, a neutral and an earth, though it used to be acceptable to use two lives and a neutral for clothes dryers, with the ground (if any) connected to the neutral. .... So you are unlikely to be able to just swap out 120v sockets for 240v sockets (they're much bigger anyway), because the existing wire only has one live core. I have heard that some sockets have two lives wires - one connected to each half of a double socket, but I have never seen one installed. |
Re: step up/down transformer
Originally Posted by ShirleyEB
(Post 12063557)
thanks jukebox widow- useful to know that my machine will be viable. It's good we can take these things rather than paying a fortune for replacement!!
|
Re: step up/down transformer
Pulaski's post #24 is correct to heed a warning...the 240VAC supply in USA/Canada is different to that in UK and could be dangerous to simply connect a UK appliance to this source....
The Canadian 3-wire 240VAC is supplied as two 120VAC live wires and one safety ground. The neutral is the phasing shift between the two live wires. Therefore, it will NOT supply a UK 240VAC appliance without some serious re-wire as the internals of these appliances are wired for one live 240VAC, one neutral and one safety ground. A transformer will work as its 240VAC output conforms to the UK 3 wire system. |
Re: step up/down transformer
Originally Posted by Davita
(Post 12074342)
Pulaski's post #24 is correct to heed a warning...the 240VAC supply in USA/Canada is different to that in UK and could be dangerous to simply connect a UK appliance to this source....
The Canadian 3-wire 240VAC is supplied as two 120VAC live wires and one safety ground. The neutral is the phasing shift between the two live wires. .... If you are correct then the difference only in presentation, because the neutral and the ground are identical any way, as both are at ground potential. |
Re: step up/down transformer
Originally Posted by Pulaski
(Post 12074582)
Are you sure? The wiring for 240v that I am used to seeing in the US has either four wires (two lives, a neutral, and a ground) or three wires (two lives and a neutral, with NO ground - IIRC this became obsolete in 1994).
If you are correct then the difference only in presentation, because the neutral and the ground are identical any way, as both are at ground potential. I thought the 4 wire system was gradually phased out...I had those plugs in my own house but that was from 30 years ago. My understanding is they used 2 phases of a 3 phase distribution system....but I'm not sure. Copy from internet... "First we do not use a 2 phase system, that proved ineffective years ago or maybe it was politics.... What we use in residential is a transformer with a secondary of 240 volts single phase center-tapped step down type. Primary voltage is generally around 2.4 KV to 7.2 KV from a 3 phase source. This allows us to serve both 120 volt loads and 240 volt loads. So our systems for single family dwellings are actually 120/240 volt single phase 3 wire sometimes called the edison system." |
Re: step up/down transformer
The subtle difference is that the neutral conductor is intended to carry a current during normal usage. In UK wiring code it's treated the same as a live conductor. The ground isn't and can in some cases be bare- and is also directly connected to the casing.
Because a UK-spec neutral is treated as a live you should get away with connecting it to one leg of a 120V system to yield a net 240V. I'm just deeply unhappy with people blithely doing it without understanding exactly what they've done.
Originally Posted by Davita
(Post 12074645)
You are correct in that a 3 wire 240VAC neutral is also grounded...but it is considered neutral as it completes the circuit to the centre tap of the grid split-phase transformer that sources the 240VAC and the 120VAC simultaneously. If the third wire just went to ground it would not allow the 120VAC to be used...that's why it is recognized as a neutral. i.e. return circuit wire to the center-tap.
I thought the 4 wire system was gradually phased out...I had those plugs in my own house but that was from 30 years ago. My understanding is they used 2 phases of a 3 phase distribution system....but I'm not sure. Copy from internet... "First we do not use a 2 phase system, that proved ineffective years ago or maybe it was politics.... What we use in residential is a transformer with a secondary of 240 volts single phase center-tapped step down type. Primary voltage is generally around 2.4 KV to 7.2 KV from a 3 phase source. This allows us to serve both 120 volt loads and 240 volt loads. So our systems for single family dwellings are actually 120/240 volt single phase 3 wire sometimes called the edison system." |
Re: step up/down transformer
Originally Posted by Pizzawheel
(Post 12074662)
The subtle difference is that the neutral conductor is intended to carry a current during normal usage. In UK wiring code it's treated the same as a live conductor. The ground isn't and can in some cases be bare- and is also directly connected to the casing. ....
.... Because a UK-spec neutral is treated as a live you should get away with connecting it to one leg of a 120V system to yield a net 240V. .... .... I'm just deeply unhappy with people blithely doing it without understanding exactly what they've done. |
Re: step up/down transformer
Originally Posted by Pulaski
(Post 12074690)
That is exactly my understanding.
I understand that to be correct, but have never done so myself. |
Re: step up/down transformer
Originally Posted by Pizzawheel
(Post 12074753)
I was considering this to run a 240V soldering iron, comforted by the fact that the iron would be supervised in use (IE never left on) and would only be used by me. The plan was kaiboshed because a spare dryer plug- which I was going to swap onto the lead in place of the 13amp one- cost over $30, more than a new soldering iron (albeit a small electronics one) on sale at crappy tire (think that was under $10)
|
Re: step up/down transformer
Originally Posted by Davita
(Post 12074803)
I can see that swopping the soldering iron plug to fit the US 240VAC dryer outlet would work, as it is a simple resistor circuit but...if a UK dryer's plug was similarly swopped .....would the UK dryer motor work?
The fact that the system was designed to have 240V/0V across it rather than +120V/-120v (excuse the simplification of AC there) is why I'd never recommend anyone do this at home. |
Re: step up/down transformer
Originally Posted by Pizzawheel
(Post 12074808)
Yes, as people have reported in this thread, you put a delta of 240V across a motor and it runs, albeit 20% faster than intended due to the frequency.
The fact that the system was designed to have 240V/0V across it rather than +120V/-120v (excuse the simplification of AC there) is why I'd never recommend anyone do this at home. |
Re: step up/down transformer
In this context I used Delta to mean differential; a voltage is always a differential. But don't get me started or I'll drift on to non-zero ground bonding.
|
Re: step up/down transformer
Originally Posted by Pizzawheel
(Post 12074808)
Yes, as people have reported in this thread, you put a delta of 240V across a motor and it runs, albeit 20% faster than intended due to the frequency.
The fact that the system was designed to have 240V/0V across it rather than +120V/-120v (excuse the simplification of AC there) is why I'd never recommend anyone do this at home. Therefore, I think we are in agreement with my response to Weve's post #23 where I suggested simply wiring his house from the N. American 240VAC system to enable using UK appliances, was a non-viable, and possibly dangerous, idea. btw...trying to get a 240VAC kettle to steam using 120VAC, as someone suggested, seems to me like watching paint dry...:lol: |
Re: step up/down transformer
Originally Posted by Davita
(Post 12075190)
Thanks Pizza...my question about the motor was rhetorical as I know it cannot be done by simply swopping the plug, and using the 240VAC split-system, as it can with a soldering iron or a kettle.
Therefore, I think we are in agreement with my response to Weve's post #23 where I suggested simply wiring his house from the N. American 240VAC system to enable using UK appliances, was a non-viable, and possibly dangerous, idea. btw...trying to get a 240VAC kettle to steam using 120VAC, as someone suggested, seems to me like watching paint dry...:lol: On the last part do the math... if R is fixed and V is reduced by 1/2 then I is 1/4 for a 3kw in the UK we can fairly assume a resistance of 20ohms the same kettle on 120v would function at approx. 750watt allowing for the same amount of energy required to boil and losses being insignificant then it would take 4 times longer to boil the same kettle isn't it interesting that most kettles in the US/Canada are around 1kw so a UK 3kw unit would only take 25% longer to boil than a local unit |
Re: step up/down transformer
Originally Posted by Pulaski
(Post 12074690)
That is exactly my understanding.
I understand that to be correct, but have never done so myself. I agree 110% with this! FWIW I have run several units on the US/Canadian twin phase 240v without issue Mainly resistive (kettles/soldering irons/heater)but some inductive (drills)without any issues I had a garage/workshop wired for both 120v and 240v with a couple of 250v 3 pin sockets (two live one earth> two horizontal pins one round earth) -'- Never bothered trying a switch mode unit as most could handle the 120v's |
Re: step up/down transformer
That's why I sarcastically suggested if waiting for a UK kettle (240VAC) to boil on 120VAC it would be like watching paint dry....I understand the math.
Are you saying you used a UK 240VAC drill on the edison split 240VAC system or the 4 wire twin-phase system.....or a Canadian 240VAC drill? |
Re: step up/down transformer
Originally Posted by Davita
(Post 12075629)
That's why I sarcastically suggested if waiting for a UK kettle (240VAC) to boil on 120VAC it would be like watching paint dry....I understand the math.
Are you saying you used a UK 240VAC drill on the edison split 240VAC system or the 4 wire twin-phase system.....or a Canadian 240VAC drill? Uk Kettle ~20ohm CAN kettle ~14ohms UK Black and Decker on CAN 250Vac at 60HZ |