220 wiring in Canada

220 wiring in Canada

Thread Tools
 
Old Jun 5th 2006, 3:04 am
  #1  
Lost again
Thread Starter
 
john fisher's Avatar
 
Joined: Aug 2005
Location: Calgary Canada
Posts: 351
john fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to behold
Default 220 wiring in Canada

I have brought out some 240v tools with me in the hope I can use the 220v system in Canada.
I understand that to get 220v you need to use the 2 hot wires, and the ground goes to earth, but what do you do with the neutral wire. or should I give up and replace tools and motor to 110v.

Help anyone.
john fisher is offline  
Old Jun 5th 2006, 4:03 am
  #2  
Born again atheist
 
Novocastrian's Avatar
 
Joined: Jul 2005
Location: Europe (to be specified).
Posts: 30,259
Novocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond reputeNovocastrian has a reputation beyond repute
Default Re: 220 wiring in Canada

Originally Posted by john fisher
I have brought out some 240v tools with me in the hope I can use the 220v system in Canada.
I understand that to get 220v you need to use the 2 hot wires, and the ground goes to earth, but what do you do with the neutral wire. or should I give up and replace tools and motor to 110v.

Help anyone.

a) get an electrician

b) you are mixing up 3-phase 220V with single phase 240V

c) Remember they're imperial volts, not metric volts

d) send an e-mail to Souvenier.....I told him I'd use that line.
Novocastrian is offline  
Old Jun 5th 2006, 12:42 pm
  #3  
Moderαtor Emeritus
 
iaink's Avatar
 
Joined: Sep 2003
Location: Upstate South Carolina
Posts: 30,768
iaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond repute
Default Re: 220 wiring in Canada

Originally Posted by john fisher
I have brought out some 240v tools with me in the hope I can use the 220v system in Canada.
I understand that to get 220v you need to use the 2 hot wires, and the ground goes to earth, but what do you do with the neutral wire. or should I give up and replace tools and motor to 110v.

Help anyone.
One of your hot lines is in effect the neutral, but your ground is not ground, thats why this is dangerous to do.

The 220 here is really two out phase 110s with a center tap ground. Either hot line to ground is 110, but hot line to hot line is 220.

The "ground" doesnt truly protect you because you would still have either 220 or 110 volts going through you depending on what else you are in contact with at any given time.

I dont think an electrician can do this to code, so if "something" happens you might have some insurance issues to deal with.
iaink is offline  
Old Jun 5th 2006, 3:23 pm
  #4  
Lost again
Thread Starter
 
john fisher's Avatar
 
Joined: Aug 2005
Location: Calgary Canada
Posts: 351
john fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to behold
Default Re: 220 wiring in Canada

Thanks for replies, I thought this my cause some trouble so I think I'll change my tool and motor on my compressor.
Or buy a few transformers, any comments on transformers.
john fisher is offline  
Old Jun 5th 2006, 3:37 pm
  #5  
Islander
 
windward's Avatar
 
Joined: Jun 2005
Location: Toronto, woo!
Posts: 953
windward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to allwindward is a name known to all
Default Re: 220 wiring in Canada

Originally Posted by john fisher
Thanks for replies, I thought this my cause some trouble so I think I'll change my tool and motor on my compressor.
Or buy a few transformers, any comments on transformers.
When I looked at them they were expensive and heavy. About £35 got me one powerful enough to charge my MD player, and with an extra adapter on the end to fit it to N. American sockets it kinda hung from the two flimsy pins in the wall rather than plugged in :|

The right kind (with a British socket output) was surprisingly difficult to find, even trawling round three separate radio shacks in Montreal, though that may just be my luck

I'm sure someone here has found a decent source...
windward is offline  
Old Jun 5th 2006, 4:02 pm
  #6  
Moderαtor Emeritus
 
iaink's Avatar
 
Joined: Sep 2003
Location: Upstate South Carolina
Posts: 30,768
iaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond repute
Default Re: 220 wiring in Canada

Originally Posted by john fisher
Thanks for replies, I thought this my cause some trouble so I think I'll change my tool and motor on my compressor.
Or buy a few transformers, any comments on transformers.
You could go down the transformer route, but if the compressor is pulling serious power, you will need a pretty big (expensive) one to have sufficient capacity.

Unless its a particularly high end piece of equipment it might be better to cut your losses and save the shipping costs too. Compressors are not that expensive here, at least those targeting the home user market, and maybe it would cost more to change the motor, who knows?

Sears or Canadian Tire probably have online prices for a replacement.

There is a place thats been mentioned here a few times for transformers, its in the US, but i cant remember the name
iaink is offline  
Old Jun 5th 2006, 4:51 pm
  #7  
Forum Regular
 
lawson44's Avatar
 
Joined: Apr 2006
Location: Bridgewater, NS
Posts: 76
lawson44 is an unknown quantity at this point
Default Re: 220 wiring in Canada

Hi

The easiest way would be to buy a generator just to power your tools, you will be able to get one with 240v and 110v outlets so you could use your UK tools and Canadian ones when you buy them in the future (if you need to use them away from a nearby power outlet).
Just check to see if yours tools are rated at 60Hz if not they will run faster than they did here which may damage them.

They are going for about $300 on ebay for a 3KW model.

I hope this helps
lawson44 is offline  
Old Jun 5th 2006, 5:09 pm
  #8  
Moderαtor Emeritus
 
iaink's Avatar
 
Joined: Sep 2003
Location: Upstate South Carolina
Posts: 30,768
iaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond repute
Default Re: 220 wiring in Canada

Originally Posted by lawson44
Hi

The easiest way would be to buy a generator just to power your tools, you will be able to get one with 240v and 110v outlets so you could use your UK tools and Canadian ones when you buy them in the future (if you need to use them away from a nearby power outlet).
Just check to see if yours tools are rated at 60Hz if not they will run faster than they did here which may damage them.

They are going for about $300 on ebay for a 3KW model.

I hope this helps
But again the "240"V from a canadian or US generator is 120, 120 and floating ground. Hence the different "twist lock" dryer type plug socket.

Buying one in the UK is an option though.

50 vs 60Hz might make a syncronous motor run a bit off speed, but probably wont do any harm. Some are rated for both, so worth looking at the plate. Just replacing them motor on a compressor might be cost effective. Places like TSC (tractor supply co...hardware for farmers or local industrial suppliers might have cheapish replacements.

Last edited by iaink; Jun 5th 2006 at 5:15 pm.
iaink is offline  
Old Jun 5th 2006, 6:55 pm
  #9  
BE Forum Addict
 
Posidrive's Avatar
 
Joined: Sep 2004
Location: Flat Oxfordshire
Posts: 1,709
Posidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond reputePosidrive has a reputation beyond repute
Default Re: 220 wiring in Canada

Originally Posted by iaink
You could go down the transformer route, but if the compressor is pulling serious power, you will need a pretty big (expensive) one to have sufficient capacity.

Unless its a particularly high end piece of equipment it might be better to cut your losses and save the shipping costs too. Compressors are not that expensive here, at least those targeting the home user market, and maybe it would cost more to change the motor, who knows?

Sears or Canadian Tire probably have online prices for a replacement.

There is a place thats been mentioned here a few times for transformers, its in the US, but i cant remember the name
http://www.voltageconverters.com

Very efficient and they also ship from within Canada
Posidrive is offline  
Old Jun 6th 2006, 2:56 pm
  #10  
Forum Regular
 
Joined: Sep 2005
Location: Bragg Creek
Posts: 76
Wild George will become famous soon enoughWild George will become famous soon enough
Default Re: 220 wiring in Canada

Originally Posted by john fisher
I have brought out some 240v tools with me in the hope I can use the 220v system in Canada.
I understand that to get 220v you need to use the 2 hot wires, and the ground goes to earth, but what do you do with the neutral wire. or should I give up and replace tools and motor to 110v.

Help anyone.

Have no idea what the f**k you are on about..how about a few ciders down
your lake this wkend Caroline???
XMrs HerbX
Wild George is offline  
Old Jun 7th 2006, 2:33 am
  #11  
Lost again
Thread Starter
 
john fisher's Avatar
 
Joined: Aug 2005
Location: Calgary Canada
Posts: 351
john fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to beholdjohn fisher is a splendid one to behold
Default Re: 220 wiring in Canada

Originally Posted by Wild George
Have no idea what the f**k you are on about..how about a few ciders down
your lake this wkend Caroline???
XMrs HerbX
There is always someone lowering the tone thread and bring alcohol online there must be a law against that.

Yes a few beers/ciders would be good (if it doesn't rain)and its not our lake .................yet, we still have another 20 days to go before we become members of the piss heads club.

To all who have made sensible replies I thank you, I think I'll change the motor on the compressor, as for the rest of my tools anyone returning to the UK, tools going cheap.
john fisher is offline  
Old Jun 8th 2006, 5:36 pm
  #12  
Forum Regular
 
Joined: Jul 2003
Posts: 204
brit_in_fizroy will become famous soon enough
Default Re: 220 wiring in Canada

Sell it all and buy new or used here. You can get the 220 from the 2 hot phases, just forget the neutral, but you will have to wire this yourself or get an electrician. ground is ground so forget the previous posts that say it isn't. The big drawback is twofold:

1. Your tools will die eventually, expecting 240 and only getting 220 means they won't work to their full potential as designed, this will mostly effect the compressor, motors will be labouring to give what you ask of them.

2. You'll only be able to use the tools where you wire them to. So I guess this means the garage or workshop.

Canada loves garage sales and pawn shops. You'll be able to get 110 stuff no problem.
brit_in_fizroy is offline  
Old Jun 8th 2006, 5:48 pm
  #13  
Moderαtor Emeritus
 
iaink's Avatar
 
Joined: Sep 2003
Location: Upstate South Carolina
Posts: 30,768
iaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond reputeiaink has a reputation beyond repute
Default Re: 220 wiring in Canada

Originally Posted by brit_in_fizroy
ground is ground .
Perhaps I was unclear. Ground is ground, but the ground on your UK equipment is potentially not going to save your bacon as its floating between the two out of phase 110s, but was designed to be common with a zero potential neutral, which you dont have jerry rigging 220 in canada. It will work, but it wont be safe, and certainly wont meet code.

UK:
wire 1 (hot) 240V AC rel to neutral and ground
wire 2 (neutral) is "return" for the hot line, zero potential to earth
wire 3 (ground) zero potential, back up for

Canada: at the distribution panel
wire 1 (hot) 110V to ground, 220V to wire 2
wire 2 (also hot) 110V to ground, 220V to wire 1
wire 3 neutral (same potential as ground)

All the 220V stuff in Canada like the dryer , cooker etc is wired with the two hot lines (isolated from the outside world), plus neutral return plus ground. The motor for the dryer and the clock and light in the oven for example need 110V, which comes from one hot and neutral, and the real power for heating is 220V from the two hot lines (no neutral). The ground and neutral are at the same potential, with the ground as a safety back up if you like

If you try wiring a UK 3 wire, (hot neutral ground) appliance, you lose the safety of the redundent back up ground. If the insulation somewhere has failed between neutral and ground, there is no consequence in the UK as they are basicaly the same potential, but here worst case you find that anything that is earthed is suddenly at 110V

Another factor in all this is do you want to try and explain what you were doing to your insurance adjuster if your house burns down for an unrelated reason?

Last edited by iaink; Jun 8th 2006 at 6:39 pm.
iaink is offline  
Old Jun 9th 2006, 12:30 am
  #14  
Part Time Poster
 
Joined: Jan 2004
Location: Worcestershire
Posts: 4,219
MikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond reputeMikeUK has a reputation beyond repute
Default Re: 220 wiring in Canada

Its do'able

but read up on how both systems are supplied..to the home, phase, earthing,

if you understand this then proceed, other wise stop, buy a tranformer, or a new motor

(in simple terms NA power is a centre taped earth, Uk is a side taped earth in terms of the supply end tranfomer)

If your system is "double insulated"(square in square symbol) then the ground is irrelevant
MikeUK is offline  
Old Jun 9th 2006, 3:08 am
  #15  
Lost in BE Cyberspace
 
macmike41's Avatar
 
Joined: Apr 2004
Location: Markham ON Canada
Posts: 5,430
macmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond reputemacmike41 has a reputation beyond repute
Default Re: 220 wiring in Canada

Isn't the phase important too - if both the 110v lines are the same phase how do you get 220v.

Originally Posted by MikeUK
Its do'able

but read up on how both systems are supplied..to the home, phase, earthing,

if you understand this then proceed, other wise stop, buy a tranformer, or a new motor

(in simple terms NA power is a centre taped earth, Uk is a side taped earth in terms of the supply end tranfomer)

If your system is "double insulated"(square in square symbol) then the ground is irrelevant