Wikiposts

Is this unsafe?

Thread Tools
 
Old Aug 20th 2013 | 4:53 pm
  #1  
Thread Starter
BE Enthusiast
 
Joined: Jun 2012
Posts: 465
From: NSW, Australia
Lucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond repute
Default Is this unsafe?

It is a rhetorical question really. Of the dangerous things I expected to see in Australia, this wasn't one of them!

Power socket immediately beneath sink (for the dishwasher) surrounded by water & waste pipes. This really bothers me and I'd like it changed.

We are renting from a terrible estate agent. They do not have a reputation for being quick (or caring).

I will need to have some sort of legal proof or regulation to refer to when I ask them to address this.

Any thoughts?

Cheers
Attached Thumbnails Is this unsafe?-p1170662.jpg  
 
Old Aug 20th 2013 | 5:21 pm
  #2  
northernbird's Avatar
Gutter Gob!!
 
Joined: Feb 2005
Posts: 13,098
From: Perth
northernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond reputenorthernbird has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by Lucas_Dad
It is a rhetorical question really. Of the dangerous things I expected to see in Australia, this wasn't one of them!

Power socket immediately beneath sink (for the dishwasher) surrounded by water & waste pipes. This really bothers me and I'd like it changed.

We are renting from a terrible estate agent. They do not have a reputation for being quick (or caring).

I will need to have some sort of legal proof or regulation to refer to when I ask them to address this.

Any thoughts?

Cheers
I agree. The plug for my dishwasher is in the cupboard next to it, away from under the sink. I'm not sure about the legality of this but it's common sense, water and electricity don't mix.
 
Old Aug 20th 2013 | 5:24 pm
  #3  
old.sparkles's Avatar
MODERATOR
 
Joined: Sep 2009
Posts: 31,928
From: Adelaide
old.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by northernbird
I agree. The plug for my dishwasher is in the cupboard next to it, away from under the sink. I'm not sure about the legality of this but it's common sense, water and electricity don't mix.
I think I'd be more worried about it being under the hose connection
 
Old Aug 20th 2013 | 5:43 pm
  #4  
brissybee's Avatar
Not actually a squirrel
 
Joined: Apr 2010
Posts: 3,446
From: England
brissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond reputebrissybee has a reputation beyond repute
Default Re: Is this unsafe?

We recently lost power because of this problem. We also had a power point under the sink, next to the dishwasher, and it got water leaked into it and threw the power throughout the house.

We got the power point blanked off by an electrician.

I wonder what might have happened had we not had a safety switch on the power board. Some houses still don't have a safety switch. Check yours does as that might be a regulation you could take to the agents... and they could blank off the under sink power point at the same time.

You could add a bit of stick by asking the agents to find out if the landlord has public liability insurance.

http://www.homehound.com.au/fact+she...sponsibilities
 
Old Aug 20th 2013 | 6:18 pm
  #5  
Amazulu's Avatar
Proudly Deplorable
 
Joined: May 2003
Posts: 24,249
From: Alloha snack bar
Amazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond reputeAmazulu has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by Lucas_Dad
It is a rhetorical question really. Of the dangerous things I expected to see in Australia, this wasn't one of them!

Power socket immediately beneath sink (for the dishwasher) surrounded by water & waste pipes. This really bothers me and I'd like it changed.

We are renting from a terrible estate agent. They do not have a reputation for being quick (or caring).

I will need to have some sort of legal proof or regulation to refer to when I ask them to address this.

Any thoughts?

Cheers
I doubt that this was wired by a sparky. If it was he should be shot - and lose his licence

Saying that, if an RCD is installed in the distribution board you will be safe
 
Old Aug 20th 2013 | 7:54 pm
  #6  
Banned
 
Joined: Jan 2011
Posts: 9,910
From: The REAL Utopia.
chris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond reputechris955 has a reputation beyond repute
Default Re: Is this unsafe?

It is illegal to wire a plug but OK to have a socket under a water supply. Its ridiculous and needs to be moved.
 
Old Aug 20th 2013 | 8:15 pm
  #7  
GarryP's Avatar
snɐןɔ ʎʇıuɐs
 
Joined: Nov 2006
Posts: 6,558
GarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond reputeGarryP has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by Lucas_Dad
It is a rhetorical question really. Of the dangerous things I expected to see in Australia, this wasn't one of them!

Any thoughts?
It's apparently legal to put a power socket in the same cupboard as the sink U bend (that's where mine is). Not sure if its legal to have them so arranged, but I'd agree its not ideal.

The basic problem is to supposedly make things 'safe' they have very prescriptive rules, and only allow 'licensed' types to do it. However, when they don't have a rule against something, those types have zero common sense to deploy - and do the quickest, most bodgy job possible (you don't want to look inside the walls at how your house is held together).

You could easily fix things by having independent inspection (which would mean you could do any work needed too, provided it met spec). However, vested interests....

This is exactly how you get the 'pink batts'. It's not a government problem as such, it's a problem of tradies having less common sense than the average sponge.
 
Old Aug 20th 2013 | 8:40 pm
  #8  
Mike at Taree's Avatar
BE Enthusiast
 
Joined: Jul 2013
Posts: 372
From: Old Bar Beach, NSW near Taree
Mike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to beholdMike at Taree is a splendid one to behold
Default Re: Is this unsafe?

I'd agree that the Australian attitude towards wiring is schizophrenic to say the least. I don't know how it still is in the UK but when I was boy scouts age one of the first things you learned was how to wire up a plug, because if you bought an electrical appliance it came with just a bare cord.

Favourite project for the annual holiday was to rewire the entire terraced house for Nanna.

I think that without this tradition, Aussies are basically ignorant of electricity .. Thank God for the RCD or the morgues would be full over here
 
Old Aug 23rd 2013 | 10:45 am
  #9  
Thread Starter
BE Enthusiast
 
Joined: Jun 2012
Posts: 465
From: NSW, Australia
Lucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond repute
Default Re: Is this unsafe?

Thanks all. I'd be surprised if this is considered legal over here, so a but more research is in order I think. I think I'll send that link (http://www.homehound.com.au/fact+she...sponsibilities) to them, along with a picture of the plug, and see what they come back with - which on past form, will be sweet FA.... until I report them to Fair Trading NSW which is what I had to do to get any action out of them last time.
 
Old Aug 23rd 2013 | 11:09 am
  #10  
Thread Starter
BE Enthusiast
 
Joined: Jun 2012
Posts: 465
From: NSW, Australia
Lucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond repute
Default Re: Is this unsafe?

Found this:

http://www.build.com.au/bathroom/bat...d-power-points

Seems to suggest to me that this power socket simply should not be there, full stop. What do you think?

This would seem to apply to the power socket that is right next to a bathroom sink too?

Final question: why the f*&^ did I move into this death trap?!!
Attached Thumbnails Is this unsafe?-p1170689.jpg  
 
Old Aug 23rd 2013 | 11:16 am
  #11  
old.sparkles's Avatar
MODERATOR
 
Joined: Sep 2009
Posts: 31,928
From: Adelaide
old.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond reputeold.sparkles has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by Lucas_Dad
Found this:

http://www.build.com.au/bathroom/bat...d-power-points

Seems to suggest to me that this power socket simply should not be there, full stop. What do you think?

This would seem to apply to the power socket that is right next to a bathroom sink too?

Final question: why the f*&^ did I move into this death trap?!!
I don't like sockets in the bathroom, but without a tape measure I'd guess that the socket is fine under Australian wiring rules. For a water container less than 45l, sockets are allowed if horizontally there are more than 0.15m away with the measurement taken from the lip of the container. Similarly, the area under a bath or sink is outside of the zones - http://www.build.com.au/bathroom/bat...d-power-points
 
Old Aug 29th 2013 | 3:16 pm
  #12  
Kelli28's Avatar
 
Joined: Apr 2004
Posts: 4,228
From: High up in Joondalup.
Kelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond reputeKelli28 has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by Lucas_Dad
Found this:

http://www.build.com.au/bathroom/bat...d-power-points

Seems to suggest to me that this power socket simply should not be there, full stop. What do you think?

This would seem to apply to the power socket that is right next to a bathroom sink too?

Final question: why the f*&^ did I move into this death trap?!!
You're out of hand wash and toothpaste
 
Old Aug 29th 2013 | 3:17 pm
  #13  
Thread Starter
BE Enthusiast
 
Joined: Jun 2012
Posts: 465
From: NSW, Australia
Lucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond reputeLucas_Dad has a reputation beyond repute
Default Re: Is this unsafe?

Originally Posted by Kelli28
You're out of hand wash and toothpaste
 
Old Sep 4th 2013 | 5:34 pm
  #14  
BE Enthusiast
 
Joined: Feb 2006
Posts: 980
From: Melbourne
The_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond repute
Default Re: Is this unsafe?

Its NOT illegal: & if its also on a safety switch theres no problem at all it may not be in the best location but as i say NOT illegal

arthur


Originally Posted by Lucas_Dad
It is a rhetorical question really. Of the dangerous things I expected to see in Australia, this wasn't one of them!

Power socket immediately beneath sink (for the dishwasher) surrounded by water & waste pipes. This really bothers me and I'd like it changed.

We are renting from a terrible estate agent. They do not have a reputation for being quick (or caring).

I will need to have some sort of legal proof or regulation to refer to when I ask them to address this.

Any thoughts?

Cheers
 
Old Sep 4th 2013 | 5:35 pm
  #15  
BE Enthusiast
 
Joined: Feb 2006
Posts: 980
From: Melbourne
The_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond repute
Default Re: Is this unsafe?

Thats illegal, it should be a min of 500mm from the bottom of the power point to the edge of the sink, you can report this to energy safe of the state your living in

Arthur

Originally Posted by Lucas_Dad
Found this:

http://www.build.com.au/bathroom/bat...d-power-points

Seems to suggest to me that this power socket simply should not be there, full stop. What do you think?

This would seem to apply to the power socket that is right next to a bathroom sink too?

Final question: why the f*&^ did I move into this death trap?!!
 


Contact Us - Archive - Advertising - Cookie Policy - Privacy Statement - Terms of Service - Your Privacy Choices

Copyright © 2026 MH Sub I, LLC dba Internet Brands. All rights reserved. Use of this site indicates your consent to the Terms of Use.