Hi All

I am hoping an Electrician can advise me on the wiring of my outside Spa, I live in Perth if that makes a difference.

I have had a quote off an Electrician for wiring up my outside spa, the Electrician has told me he is going to install a 15 amp socket, to do this he is going to also install a new RCD feeding a 16Amp MCB then feeding my new 15Amp Socket with 2.5mm cable.

Now I have two RCD's already installed in my Electric box, would one of these RCD's be able to be used or does you require a separate circuit for the SPA inc the RCD, MCB etc?

I am asking this because I got totally ripped off last time I had work done and even though I want everything done safely and correct I dont want to be ripped off.

Thanks Don
slingshot69 is offline  
Old Aug 26th 2007, 11:13 am
  #2  
Forum Regular
 
Joined: Apr 2007
Posts: 124
noggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to allnoggin is a name known to all
Default Re: Electrical Wiring Of A Outside Spa

hi mate, check your fuse board....2rcds? what ratings...didnt thint they did split boards in oz?...do they?..if u have 2rcds at present where the hell is he going to put the third?
noggin is offline  
Old Aug 26th 2007, 11:58 am
  #3  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by noggin
hi mate, check your fuse board....2rcds? what ratings...didnt thint they did split boards in oz?...do they?..if u have 2rcds at present where the hell is he going to put the third?
Hi

There are 2 RCD's, its not very well marked so I cant tell you much more there sorry.
slingshot69 is offline  
Old Aug 26th 2007, 12:00 pm
  #4  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by noggin
hi mate, check your fuse board....2rcds? what ratings...didnt thint they did split boards in oz?...do they?..if u have 2rcds at present where the hell is he going to put the third?
He was saying about the RCD feeding the Spa?
slingshot69 is offline  
Old Aug 26th 2007, 1:05 pm
  #5  
Account Closed
 
Joined: Jan 2004
Posts: 32
devtrend is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by slingshot69
Hi All

I am hoping an Electrician can advise me on the wiring of my outside Spa, I live in Perth if that makes a difference.

I have had a quote off an Electrician for wiring up my outside spa, the Electrician has told me he is going to install a 15 amp socket, to do this he is going to also install a new RCD feeding a 16Amp MCB then feeding my new 15Amp Socket with 2.5mm cable.

Now I have two RCD's already installed in my Electric box, would one of these RCD's be able to be used or does you require a separate circuit for the SPA inc the RCD, MCB etc?

I am asking this because I got totally ripped off last time I had work done and even though I want everything done safely and correct I dont want to be ripped off.

Thanks Don
That sounds right to me, the spa will probably pull a fair amount of current due to the heaters.

Its a good idea to keep things like that separate, it could be wired into your existing sockets circuit but you may start getting nuisance trips etc.

How much is the quote?
devtrend is offline  
Old Aug 26th 2007, 1:30 pm
  #6  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by devtrend
That sounds right to me, the spa will probably pull a fair amount of current due to the heaters.

Its a good idea to keep things like that separate, it could be wired into your existing sockets circuit but you may start getting nuisance trips etc.

How much is the quote?
Yes I can understand the circuit being seperate but I was just wondering why the extra RCD, I just wanted some more advice, picking peoples brains
slingshot69 is offline  
Old Aug 26th 2007, 7:55 pm
  #7  
Forum Regular
 
Graff's Avatar
 
Joined: Feb 2007
Location: Tamworth U.K.- Brisbane Very Soon Now Visa Granted!!
Posts: 73
Graff will become famous soon enough
Default Re: Electrical Wiring Of A Outside Spa

If you have 2 RCD's in the same fuse board, one as the main switch which may be 100 m\a trip current the other 30 m\a trip, which is normally stamped on the front. You will have this if you have a TT system, Where you have a earth rod, so your main earth comming into your house is not supplied by your electric supplier. Steve 'o' on the electrical forum would know as he is over Oz and he knows everything . give him a shout.
Graff is offline  
Old Aug 26th 2007, 8:32 pm
  #8  
Worongary
 
steve`o's Avatar
 
Joined: Sep 2005
Location: GC hinterland
Posts: 10,288
steve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond repute
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by Graff
If you have 2 RCD's in the same fuse board, one as the main switch which may be 100 m\a trip current the other 30 m\a trip, which is normally stamped on the front. You will have this if you have a TT system, Where you have a earth rod, so your main earth comming into your house is not supplied by your electric supplier. Steve 'o' on the electrical forum would know as he is over Oz and he knows everything . give him a shout.
not everything

ususally the main rcd ( safety switch over here is rated at 30ma )
so if it has a main safety switch rated at 30ma its a pointless exercise fitting another

check your fuse board and read what it says on the rcds look for mA rating and A rating


regards steve
steve`o is offline  
Old Aug 26th 2007, 11:20 pm
  #9  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by steve`o
not everything

ususally the main rcd ( safety switch over here is rated at 30ma )
so if it has a main safety switch rated at 30ma its a pointless exercise fitting another

check your fuse board and read what it says on the rcds look for mA rating and A rating


regards steve
Hi

Thanks for all the help.

They both say 40amp and 30ma, does that tell you anything.

Thanks Don
slingshot69 is offline  
Old Aug 27th 2007, 1:01 am
  #10  
BE Enthusiast
 
Joined: Feb 2006
Location: Melbourne
Posts: 980
The_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond reputeThe_Pom_From_Aus has a reputation beyond repute
Default Re: Electrical Wiring Of A Outside Spa

slingshot69;
regards to your Spa the RCD must be installed i have a concern about the bloke fitting the 2.5mm cable, the cable size depends on the heater element size also the distance from the switchboard to the Spa,i dont think a 2.5mm cable is noway near enough. at the leat you would need a 4.00mm cable as i say depending on the distance there will be a volt drop, on my own Spa (electrical) my heater is 5 KW and the distance is some 30 meters from the switchboard so i had to install a 6.00mm cable via a RCD for safety requirements. you can get a 20amp 30m/a RCD or if the Spa is drawing more than 20amp you get a 40amp 30m/a RCD. if you done have any spare ways in the switchboard you can always have another board installed next to the existing one or maybe upgrade the existing board to a larger capacity, allowing for future expansion.

regards

arthur
The_Pom_From_Aus is offline  
Old Aug 27th 2007, 4:28 am
  #11  
Worongary
 
steve`o's Avatar
 
Joined: Sep 2005
Location: GC hinterland
Posts: 10,288
steve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond reputesteve`o has a reputation beyond repute
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by slingshot69
Hi

Thanks for all the help.

They both say 40amp and 30ma, does that tell you anything.

Thanks Don
yeah its sounds like they are subcircuits and not the main safety swithc so yes you wil need a rcd/mcb combination fitting, although like arthur i would be concerned at a 2.5mm cable being sufficeint to power a spa ( unless of course its gas fired or solar )

ca you tell us the power requirements for the spa
( the supplier should be able to give you either an ampage or wattage )

regards steve
steve`o is offline  
Old Aug 27th 2007, 4:51 am
  #12  
I don't re Member
 
andrew63's Avatar
 
Joined: May 2004
Location: Termite Country (Tanah Merah)
Posts: 1,372
andrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond reputeandrew63 has a reputation beyond repute
Default Re: Electrical Wiring Of A Outside Spa

Not sure if this will be useful but my spa plugs into a 15 amp socket but the plug itself contains a RCD type flick switch. Maybe they can be used as an alternative to fitting one on the fuse box?

Andrew
andrew63 is offline  
Old Aug 27th 2007, 5:07 am
  #13  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by The_Pom_From_Aus
slingshot69;
regards to your Spa the RCD must be installed i have a concern about the bloke fitting the 2.5mm cable, the cable size depends on the heater element size also the distance from the switchboard to the Spa,i dont think a 2.5mm cable is noway near enough. at the leat you would need a 4.00mm cable as i say depending on the distance there will be a volt drop, on my own Spa (electrical) my heater is 5 KW and the distance is some 30 meters from the switchboard so i had to install a 6.00mm cable via a RCD for safety requirements. you can get a 20amp 30m/a RCD or if the Spa is drawing more than 20amp you get a 40amp 30m/a RCD. if you done have any spare ways in the switchboard you can always have another board installed next to the existing one or maybe upgrade the existing board to a larger capacity, allowing for future expansion.

regards

arthur

Hi Arthur

Thanks for running through that for me, I want to check a few things out with this guy to make sure the cable size etc. The spa is going to be at the furthest point from my switch board.

I also think there is only one spare way left and thats for an MCB.

Thanks again, Don
slingshot69 is offline  
Old Aug 27th 2007, 5:09 am
  #14  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by steve`o
yeah its sounds like they are subcircuits and not the main safety swithc so yes you wil need a rcd/mcb combination fitting, although like arthur i would be concerned at a 2.5mm cable being sufficeint to power a spa ( unless of course its gas fired or solar )

ca you tell us the power requirements for the spa
( the supplier should be able to give you either an ampage or wattage )

regards steve
Hi Steve

Thanks for the advice, I am away on a job at the moment so I cant get you the info, I would of thought it would be on the Spa somewhere but I wont know until next week.

Thanks again, Don
slingshot69 is offline  
Old Aug 27th 2007, 5:11 am
  #15  
Just Joined
Thread Starter
 
Joined: Aug 2007
Posts: 24
slingshot69 is an unknown quantity at this point
Default Re: Electrical Wiring Of A Outside Spa

Originally Posted by andrew63
Not sure if this will be useful but my spa plugs into a 15 amp socket but the plug itself contains a RCD type flick switch. Maybe they can be used as an alternative to fitting one on the fuse box?

Andrew

Hi Andrew

That sounds interesting especially as I dont think an RCD will fit in my board, I would like to see what the others think of this idea.

Thanks Don