Steerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Nutek


Hanging on the side of my house. Pull down to switch to the generator.
Looks very straight-forward, but .... aren't the two big fat black wires at the top the two 'phases' of the three-phase utility supply, whereas, the red/black at the bottom represent the single-phase from a generator? Is that kosher? Or - noticing the sticker 'LINE' above the 'left' wire, perhaps the left wire is one phase from the utility, while the right-hand wire is 'neutral'; that would make more sense, in terms of having the generator 'red' wire going to the 'LINE' feed, and the black wire going to the 'neutral' feed. But if that is the case, what happens to the 'other' phase coming into your home? Most homes have two phases coming in from the utility. Are you simply feeding the generator into one of the two phases, and then accepting that only 'half' of your home breakers are going to be 'life' in an outage?

Also - is this a simple example of a 'transfer switch'? Looks like it to me!
Steerpike is offline  
Old Aug 14th 2021, 11:39 pm
  #32  
tht
DE-UK-NZ-IE-US... the TYP
 
Joined: Mar 2010
Posts: 2,855
tht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Nutek


Hanging on the side of my house. Pull down to switch to the generator.
That red and black wire look very thin, it can’t be a very high KW generator? I have a 100amp circuit and the wires are much thicker than that.
tht is offline  
Old Aug 14th 2021, 11:50 pm
  #33  
 
Nutek's Avatar
 
Joined: Apr 2012
Location: CT
Posts: 33,495
Nutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by tht
That red and black wire look very thin, it can’t be a very high KW generator? I have a 100amp circuit and the wires are much thicker than that.
It’s 10/4 but yeah, it needs replacing. 50 amp receptacle on the other end. Previous owner put it in.

we have never used it but we are looking at getting a new generator so I would want to swap that out at the same time. The rest of it seems ok.
Nutek is offline  
Old Aug 15th 2021, 8:21 pm
  #34  
 
Nutek's Avatar
 
Joined: Apr 2012
Location: CT
Posts: 33,495
Nutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Steerpike
Looks very straight-forward, but .... aren't the two big fat black wires at the top the two 'phases' of the three-phase utility supply, whereas, the red/black at the bottom represent the single-phase from a generator? Is that kosher? Or - noticing the sticker 'LINE' above the 'left' wire, perhaps the left wire is one phase from the utility, while the right-hand wire is 'neutral'; that would make more sense, in terms of having the generator 'red' wire going to the 'LINE' feed, and the black wire going to the 'neutral' feed. But if that is the case, what happens to the 'other' phase coming into your home? Most homes have two phases coming in from the utility. Are you simply feeding the generator into one of the two phases, and then accepting that only 'half' of your home breakers are going to be 'life' in an outage?

Also - is this a simple example of a 'transfer switch'? Looks like it to me!
Single Phase. Those two thick wires carry 120V each You need another one for 3 phase.

[edit] Yeah.. Simple (old) transfer switch.
Nutek is offline  
Old Aug 16th 2021, 3:28 pm
  #35  
tht
DE-UK-NZ-IE-US... the TYP
 
Joined: Mar 2010
Posts: 2,855
tht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond reputetht has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Nutek
It’s 10/4 but yeah, it needs replacing. 50 amp receptacle on the other end. Previous owner put it in.

we have never used it but we are looking at getting a new generator so I would want to swap that out at the same time. The rest of it seems ok.
The one I have to connect the 50amp 240v from the generator to the receptacle on the house is really thick, but I assume most of it is just to protect it.

It’s interesting what others said about not running AC. I was not sure ours would work, we have a gas stove and dryer, so when I have run this I did not really shut any thing off. I can definitely hear it work harder once the AC comes on, but it worked and managed to run that and everything else. I brought a smaller LPG unit for my other house, but it’s only 120v so I don’t think it can run my well pump… back to looking at solar and a power wall or 2 (assuming that can get through the night).




tht is offline  
Old Aug 16th 2021, 4:02 pm
  #36  
BE Commentator
 
S Folinsky's Avatar
 
Joined: Feb 2010
Location: Los Angeles, California
Posts: 8,424
S Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Steerpike
Looks very straight-forward, but .... aren't the two big fat black wires at the top the two 'phases' of the three-phase utility supply, whereas, the red/black at the bottom represent the single-phase from a generator? Is that kosher? Or - noticing the sticker 'LINE' above the 'left' wire, perhaps the left wire is one phase from the utility, while the right-hand wire is 'neutral'; that would make more sense, in terms of having the generator 'red' wire going to the 'LINE' feed, and the black wire going to the 'neutral' feed. But if that is the case, what happens to the 'other' phase coming into your home? Most homes have two phases coming in from the utility. Are you simply feeding the generator into one of the two phases, and then accepting that only 'half' of your home breakers are going to be 'life' in an outage?

Also - is this a simple example of a 'transfer switch'? Looks like it to me!
Just upgraded the service on my house. Department of Water & Power did a “meter spot” and our 1938 power drop had to be relocated. So new main panel on north side of house with old panel on south side converted to a sub panel. I like to have basic knowledge of my house’s systems.

So, the power drop consists of the two black lines of 120 v each and the bare ground/neutral wire. I see that there appears to be a grounding cable coming out of the bottom. I presume that the conduit to the right hooks up to the meter.

This installation strikes me as a “Mickey Mouse” conversion of the house cutoff into a transfer switch. Betcha it ain’t legal.
S Folinsky is offline  
Old Aug 16th 2021, 5:18 pm
  #37  
Lost in BE Cyberspace
 
Steerpike's Avatar
 
Joined: Nov 2007
Location: Bay Area, CA
Posts: 13,111
Steerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond reputeSteerpike has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by S Folinsky
Just upgraded the service on my house. Department of Water & Power did a “meter spot” and our 1938 power drop had to be relocated. So new main panel on north side of house with old panel on south side converted to a sub panel. I like to have basic knowledge of my house’s systems.

So, the power drop consists of the two black lines of 120 v each and the bare ground/neutral wire. I see that there appears to be a grounding cable coming out of the bottom. I presume that the conduit to the right hooks up to the meter.

This installation strikes me as a “Mickey Mouse” conversion of the house cutoff into a transfer switch. Betcha it ain’t legal.
I need to clarify / fess up that I was completely wrong above - typical houses do NOT get 'two phases' fed to them from the utility; they get two 120V lines, which are fed from a center-tapped winding on a transformer at/near the utility pole, which is fed by a single-phase of the utility source; correctly referred to by Nutek as 'split phase'.

I found this diagram online that really helped: Note, the 'flow' is from right to left (utility pole on the right, house on the left):


The question I still have for Nutek is what is the voltage generated by his generator; if his generator is 240V, then that makes sense - that is, the red and black wires coming into his 'transfer box' at the bottom are each 120V relative to ground, or 240V relative to each other. If the generator is only 120V (which I originally assumed when I replied above) then I don't understand how it could work. I've asked Nutek for more details by PM. Hopefully we can clarify here when resolved!
Steerpike is offline  
Old Aug 16th 2021, 5:42 pm
  #38  
BE Commentator
 
S Folinsky's Avatar
 
Joined: Feb 2010
Location: Los Angeles, California
Posts: 8,424
S Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond reputeS Folinsky has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Steerpike
I need to clarify / fess up that I was completely wrong above - typical houses do NOT get 'two phases' fed to them from the utility; they get two 120V lines, which are fed from a center-tapped winding on a transformer at/near the utility pole, which is fed by a single-phase of the utility source; correctly referred to by Nutek as 'split phase'.

I found this diagram online that really helped: Note, the 'flow' is from right to left (utility pole on the right, house on the left):


The question I still have for Nutek is what is the voltage generated by his generator; if his generator is 240V, then that makes sense - that is, the red and black wires coming into his 'transfer box' at the bottom are each 120V relative to ground, or 240V relative to each other. If the generator is only 120V (which I originally assumed when I replied above) then I don't understand how it could work. I've asked Nutek for more details by PM. Hopefully we can clarify here when resolved!
Curiously, while we’ve been doing all the work on our house, LADWP updated the grid in our neighborhood. The linemen informed me that the high tension line before the transformers was 4200 volts.

Another thing I learned, and can be seen in Nutek’s box is that neutral and ground are bridged up until the main box. Sub panels are not bridged.
S Folinsky is offline  
Old Aug 16th 2021, 7:06 pm
  #39  
BE Enthusiast
 
helwardman's Avatar
 
Joined: Oct 2008
Location: Louisiana
Posts: 615
helwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond reputehelwardman has a reputation beyond repute
Default Re: Standby Generators

Portable generators of that type are typically 240VAC.
helwardman is offline  
Old Aug 17th 2021, 12:00 pm
  #40  
 
Nutek's Avatar
 
Joined: Apr 2012
Location: CT
Posts: 33,495
Nutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by S Folinsky

Betcha it ain’t legal.
Passed inspection with no problems at all. Though I am looking to change it for a newer (and better) setup.

Nutek is offline  
Old Aug 17th 2021, 12:03 pm
  #41  
 
Nutek's Avatar
 
Joined: Apr 2012
Location: CT
Posts: 33,495
Nutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Steerpike
I need to clarify / fess up that I was completely wrong above - typical houses do NOT get 'two phases' fed to them from the utility; they get two 120V lines, which are fed from a center-tapped winding on a transformer at/near the utility pole, which is fed by a single-phase of the utility source; correctly referred to by Nutek as 'split phase'.

I found this diagram online that really helped: Note, the 'flow' is from right to left (utility pole on the right, house on the left):


The question I still have for Nutek is what is the voltage generated by his generator; if his generator is 240V, then that makes sense - that is, the red and black wires coming into his 'transfer box' at the bottom are each 120V relative to ground, or 240V relative to each other. If the generator is only 120V (which I originally assumed when I replied above) then I don't understand how it could work. I've asked Nutek for more details by PM. Hopefully we can clarify here when resolved!
Haven't purchased yet but yeah, 50amp 240VAC
Nutek is offline  
Old Aug 17th 2021, 2:11 pm
  #42  
BE Forum Addict
 
Joined: Jun 2015
Location: Near Lynchburg Tennessee, home of Jack Daniels
Posts: 1,381
ddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Nutek
It’s 10/4 but yeah, it needs replacing. 50 amp receptacle on the other end. Previous owner put it in.

we have never used it but we are looking at getting a new generator so I would want to swap that out at the same time. The rest of it seems ok.
The problem I see with the switch is the generator will
run directly to main panel with no breaker protection. The #10 wire can carry 30 amps but at the main panel it could be carrying the whole house. Also power companies are very particular about how long the feed wire is from meter to main panel. This wire is unfused and could burn/melt if it got shorted out.

ddsrph is offline  
Old Aug 17th 2021, 2:15 pm
  #43  
 
Nutek's Avatar
 
Joined: Apr 2012
Location: CT
Posts: 33,495
Nutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by ddsrph
The problem I see with the switch is the generator will
run directly to main panel with no breaker protection. The #10 wire can carry 30 amps but at the main panel it could be carrying the whole house. Also power companies are very particular about how long the feed wire is from meter to main panel. This wire is unfused and could burn/melt if it got shorted out.
Correct, hence my desire to make changes once I figure out my best options. (Bear in mind this is currently (heh) unused)).

[Edit to add] The panel itself is directly behind the switch, on the other side of the wall.

Last edited by Nutek; Aug 17th 2021 at 2:17 pm.
Nutek is offline  
Old Aug 17th 2021, 2:21 pm
  #44  
BE Forum Addict
 
Joined: Jun 2015
Location: Near Lynchburg Tennessee, home of Jack Daniels
Posts: 1,381
ddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond reputeddsrph has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by Nutek
Correct, hence my desire to make changes once I figure out my best options. (Bear in mind this is currently (heh) unused)).
I am interested in learning more about how modern transfer switches work. If convenient to do so seems like a lockout device would be the way to go unless a whole house generator is being installed.
ddsrph is offline  
Old Aug 17th 2021, 2:48 pm
  #45  
 
Nutek's Avatar
 
Joined: Apr 2012
Location: CT
Posts: 33,495
Nutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond reputeNutek has a reputation beyond repute
Default Re: Standby Generators

Originally Posted by ddsrph
I am interested in learning more about how modern transfer switches work. If convenient to do so seems like a lockout device would be the way to go unless a whole house generator is being installed.
An Interlock Kit is really the way to go. It would take some considerable re-jigging on my (full) panel to do it though. Still... I may decide to go that way.