Hello everyone! I'm a 'leccy from UK. Worked for Home Depot for 2 years....OMG.
Typical questions.......Why can't I join 30A to 50A wire????
If I take a 15A breaker out, can't I put a 50A breaker in, because it keeps tripping
Its ok, I'm only running 1000 ft of wire (Voltage Drop)
Have fun you Eleccys
Typical questions.......Why can't I join 30A to 50A wire????
If I take a 15A breaker out, can't I put a 50A breaker in, because it keeps tripping
Its ok, I'm only running 1000 ft of wire (Voltage Drop)
Have fun you Eleccys
#2
BE Enthusiast
Joined: Feb 2006
Location: Melbourne
Posts: 980
Re: Beware if you come to Texas
lanky
if you change the C/B & increase the current rating then you must ensure the actual cable is capable of taking the 50A current.
also check the current rating of the appliance or the load its drawing.
if you change the C/B & increase the current rating then you must ensure the actual cable is capable of taking the 50A current.
also check the current rating of the appliance or the load its drawing.