Is this unsafe?
#16
Re: Is this unsafe?
I thought that horizontally it looked to be at least 150mm from the internal lip of the sink, and therefore outside of the zone. Plus on a sink of 45l, the vertical distyance would be 400mm
#17
BE Enthusiast
Thread Starter
Joined: Jun 2012
Location: NSW, Australia
Posts: 450
Re: Is this unsafe?
An electrician moved the socket, but only to the side of the sink's cabinet. I'm not at all convinced that it is safe, but the estate agent comprises a bunch of giveashitless idiots. If there's no law saying that it is a bad job, I guess I've little choice but to wait for the leak, spark, and house to burn down.
#18
BE Enthusiast
Joined: Feb 2006
Location: Melbourne
Posts: 980
Re: Is this unsafe?
Sorry for any confusion mate:
Now then the state of play is this 1st its to close to the sink, it must be 500mm away from the edge of the sink (Thats the Law) the other thing is it must be in a timber cabinet if its that close to the sink. the cabinet is classed as a barrier.(Next) the power point must be protected at the switchboard (Fuse box) with whats called an RCD (Safety Switch) again that's the law if not then get onto the estate agent telling then this contravenes the AS/NZ Electrical wiring rules. that's there problem. if you still don't get any Joy call energy safe in the state you reside in & they shall investigate this for you Free of charge. if your in Melbourne contact me & i can easily start the ball rolling with Energy safe Victoria its not hard at all once you tell the estate agents you have concerns for safety & you intend to contact energy safe they shall shit them self. remember to keep records of all communication with your real estate people.
Arthur in Melbourne
Now then the state of play is this 1st its to close to the sink, it must be 500mm away from the edge of the sink (Thats the Law) the other thing is it must be in a timber cabinet if its that close to the sink. the cabinet is classed as a barrier.(Next) the power point must be protected at the switchboard (Fuse box) with whats called an RCD (Safety Switch) again that's the law if not then get onto the estate agent telling then this contravenes the AS/NZ Electrical wiring rules. that's there problem. if you still don't get any Joy call energy safe in the state you reside in & they shall investigate this for you Free of charge. if your in Melbourne contact me & i can easily start the ball rolling with Energy safe Victoria its not hard at all once you tell the estate agents you have concerns for safety & you intend to contact energy safe they shall shit them self. remember to keep records of all communication with your real estate people.
Arthur in Melbourne
Thanks for the replies Arthur but I'm a bit confused - you've said it is both illegal and not illegal?
An electrician moved the socket, but only to the side of the sink's cabinet. I'm not at all convinced that it is safe, but the estate agent comprises a bunch of giveashitless idiots. If there's no law saying that it is a bad job, I guess I've little choice but to wait for the leak, spark, and house to burn down.
An electrician moved the socket, but only to the side of the sink's cabinet. I'm not at all convinced that it is safe, but the estate agent comprises a bunch of giveashitless idiots. If there's no law saying that it is a bad job, I guess I've little choice but to wait for the leak, spark, and house to burn down.
#19
Re: Is this unsafe?
Sorry for any confusion mate:
Now then the state of play is this 1st its to close to the sink, it must be 500mm away from the edge of the sink (Thats the Law) the other thing is it must be in a timber cabinet if its that close to the sink. the cabinet is classed as a barrier.(Next) the power point must be protected at the switchboard (Fuse box) with whats called an RCD (Safety Switch) again that's the law if not then get onto the estate agent telling then this contravenes the AS/NZ Electrical wiring rules. that's there problem. if you still don't get any Joy call energy safe in the state you reside in & they shall investigate this for you Free of charge. if your in Melbourne contact me & i can easily start the ball rolling with Energy safe Victoria its not hard at all once you tell the estate agents you have concerns for safety & you intend to contact energy safe they shall shit them self. remember to keep records of all communication with your real estate people.
Arthur in Melbourne
Now then the state of play is this 1st its to close to the sink, it must be 500mm away from the edge of the sink (Thats the Law) the other thing is it must be in a timber cabinet if its that close to the sink. the cabinet is classed as a barrier.(Next) the power point must be protected at the switchboard (Fuse box) with whats called an RCD (Safety Switch) again that's the law if not then get onto the estate agent telling then this contravenes the AS/NZ Electrical wiring rules. that's there problem. if you still don't get any Joy call energy safe in the state you reside in & they shall investigate this for you Free of charge. if your in Melbourne contact me & i can easily start the ball rolling with Energy safe Victoria its not hard at all once you tell the estate agents you have concerns for safety & you intend to contact energy safe they shall shit them self. remember to keep records of all communication with your real estate people.
Arthur in Melbourne
#20
BE Enthusiast
Joined: Feb 2006
Location: Melbourne
Posts: 980
Re: Is this unsafe?
Again, gonna disagree. Sinks less than 45l capacity would have a zone 2 limited by 150mm horizontally, and 400mm vertically. Only above 45l would the zone be extended to 500mm horizontally and 1m vertically as is indicated in the images on the link provided - http://www.build.com.au/bathroom/bat...d-power-points.
look at the distance of the power point to the edge of the sink tell me if that's a class 2 ask energy safe they shall tell you it requires a barrier, or ask PEER they shall tell you
Arthur
#21
Re: Is this unsafe?
I know, and that would be true if it was still in zone 2 - but it is outside of zone 2 and since there are no other zones associated with fixed water containers it's fine. [6.2.4.2]
Last edited by old.sparkles; Sep 5th 2013 at 9:40 am.