vetasses practical tools?
#1
Forum Regular
Thread Starter
Joined: Jan 2011
Location: Essex uk
Posts: 30
vetasses practical tools?
Hi all i have got my vetassesment this coming monday in London, i am hoping to go on my bike. Can any body advise me on what tools to take as i have limited bag space.
many thanks
many thanks
#2
Forum Regular
Joined: Feb 2011
Location: Egremont, Cumbria
Posts: 59
Re: vetasses practical tools?
See you there pal. Are you nervous, cos I am!
#5
Forum Regular
Joined: Sep 2009
Posts: 53
Re: vetasses practical tools?
No no no Jockstar, remember to TEST your meter then Test your meter on the known source, then Test your meter then Test your meter you cant TEST it enough, you must allways check the meter !!!!!!. When I did mine it was a guy called Roger ( nice fella who puts you at ease ) he was red hot on the safe isolation ( do it as in the Vetassess down load ) I dont think you can take it in to the practical but i maybe wrong. The AM2 is a lot worse mate this is more your part P I have been informed.
ER
ER
#6
Re: vetasses practical tools?
No no no Jockstar, remember to TEST your meter then Test your meter on the known source, then Test your meter then Test your meter you cant TEST it enough, you must allways check the meter !!!!!!. When I did mine it was a guy called Roger ( nice fella who puts you at ease ) he was red hot on the safe isolation ( do it as in the Vetassess down load ) I dont think you can take it in to the practical but i maybe wrong. The AM2 is a lot worse mate this is more your part P I have been informed.
ER
ER
#7
Re: vetasses practical tools?
No no no Jockstar, remember to TEST your meter then Test your meter on the known source, then Test your meter then Test your meter you cant TEST it enough, you must allways check the meter !!!!!!. When I did mine it was a guy called Roger ( nice fella who puts you at ease ) he was red hot on the safe isolation ( do it as in the Vetassess down load ) I dont think you can take it in to the practical but i maybe wrong. The AM2 is a lot worse mate this is more your part P I have been informed.
ER
ER
steve
#8
Re: vetasses practical tools?
No no no Jockstar, remember to TEST your meter then Test your meter on the known source, then Test your meter then Test your meter you cant TEST it enough, you must allways check the meter !!!!!!. When I did mine it was a guy called Roger ( nice fella who puts you at ease ) he was red hot on the safe isolation ( do it as in the Vetassess down load ) I dont think you can take it in to the practical but i maybe wrong. The AM2 is a lot worse mate this is more your part P I have been informed.
ER
ER
You can use a known live supply to prove your meter instead of a proving unit(ie feed side of the main switch will still be live when it is switched off )
As in AS/NZS 4836:2001
6.3 TEST EQUIPMENT CHECKS
When voltage detectors such as voltage testers are used to prove de-energization, they shall
be tested for correct operation immediately before use, and again immediately after use,
particularly if the test result indicates zero voltage, to confirm that the instrument is still
working correctly.
Test equipment shall be checked for accuracy of operation at appropriate intervals
#9
Forum Regular
Joined: Feb 2011
Location: Egremont, Cumbria
Posts: 59
Re: vetasses practical tools?
Heres a link to the General Electrician page, which has the isolation/reconnection process http://www.vetassess.com.au/download...0(General).pdf
#10
Re: vetasses practical tools?
Heres a link to the General Electrician page, which has the isolation/reconnection process http://www.vetassess.com.au/download...0(General).pdf
Electrical Disconnection and Reconnection Process
Disconnection process to be demonstrated on the day of assessment.
(Steps in bold are critical in the process)
Personnel to be notified in immediate area that you are to commence disconnection and interruption to supply.
Will removal of protective devices affect essential services?
Test voltage tester at known 'LIVE' source for correct operation before use.
Ensure the frame of the equipment is not 'LIVE' by testing between frame/chassis and the known earth.
Test voltage tester at known 'LIVE' source for correct operation after use.
Take operational details of appliance. Eg. kW and voltage.
Take direction of rotation (DOR) of motor (where applicable).
Complete details on danger tags. Eg. Name, date, fault, etc.
Affix danger tags to isolation points. Eg. appliance, isolating switch, switchboard, etc.
Determine location of appropriate protective device.
Do not leave exposed 'LIVE' terminals/conductors at switchboard or appliance.
Test voltage tester at known 'LIVE' source for correct operation before use.
Before touching appliance conductors, test for 'LIVE' Test between - all conductors and known earth.
This test also includes testing for 'LIVE' between the protective earthing conductor and the known earth.
The appliance conductors must also be tested for 'LIVE' by testing between all conductors. This includes the protective earthing conductor.
Test voltage tester for correct operation on known 'LIVE' source after using it. (Fail only occurs when previous test indicated terminals/conductors were de-energised).
Isolate protective device by applying lock-dog and lock or inserting ‘dummy’ fuse wedge in fuse base.
Terminate conductors in approved manner and enclose in junction box. Cable ends must be fully insulated.
Affix Danger Tag to terminated conductors enclosed in junction box.
Ensure terminated conductors are protected against mechanical damage.
Clean up work area and notify personnel.
Reconnection process to be demonstrated on the day of assessment.
(Steps in bold are critical in the process)
Notify personnel of return to work site.
Ensure the appliance to be reconnected is of the same operational ratings. Eg. kW, amperes, voltage, etc.
Test Insulation Resistance & Continuity tester on both Meg Ohm (500V) and Ohm scale for correct operation.
Carry out the insulation resistance test of the appliance. Test between all active and neutral conductors to the earth contact of the appliance.
• Not containing sheathed heating elements – Not less than 1 Meg Ω
• Containing sheathed heating elements – Not less than 0.01 Meg Ω
Before touching final sub-circuit conductors, test for 'LIVE' Test between - all conductors and the known earth. This test also includes testing for 'LIVE' between the protective earthing conductor and the effective earth.
The final sub-circuit conductors must also be tested for 'LIVE' by testing between all conductors. This includes the protective earthing conductor.
Test voltage tester for correct operation on known 'LIVE' source after using it. (Fail only occurs when previous test indicated terminals/conductors were de-energised).
Reconnect final sub-circuit wiring to appliance terminals.
Carry out continuity test on final sub-circuit protective earthing conductor from effective earth to frame of appliance. (This test should be carried out after the circuit conductors have been connected to the equipment terminals and before the power has been restored).
Notify personnel of restoration of power.
Do not leave exposed 'LIVE' terminals/conductors at switchboard or appliance.
Remove lock, lock-dog and switch on circuit breaker or insert correct fuse wedge to restore power.
Check appliance for correct operation. Eg DOR. (Direction of Rotation).
Clean up work area and notify personnel.
Note: Testing the voltage tester for correct operation after use is critical when the candidate is going to touch the conductors/components on the belief they are de-energised.
#11
Forum Regular
Thread Starter
Joined: Jan 2011
Location: Essex uk
Posts: 30
Re: vetasses practical tools?
Hey all had vetassessment on Monday, I think all went well!
The assessor Dean was a good bloke for an ozzy ha, hi Dean, he says he looks at these forums sometimes.
The day goes pretty much as others have described on this forum, thanks to them for bothering to take the time to describe there day.
With regards to the tools bring what the prep sheet which will be issued to you prior to your lovely day out.ha
I would also take pipe cutters and small level,
Swat up on ohms law, 3phase power, capacitance,inductance, 1st year stuff only 20 questions.
Safe isolation it's piss easy just keep testing for potentially live and keep checking your testers, keep talking yourself though every process and pretend that the fuseboard is in another room.
Start stop motor circuit is a dodle just follow the drawing you can't go wrong.
Hope this helps.
Also met some nice guys there good luck to them
All the best
Shaun
The assessor Dean was a good bloke for an ozzy ha, hi Dean, he says he looks at these forums sometimes.
The day goes pretty much as others have described on this forum, thanks to them for bothering to take the time to describe there day.
With regards to the tools bring what the prep sheet which will be issued to you prior to your lovely day out.ha
I would also take pipe cutters and small level,
Swat up on ohms law, 3phase power, capacitance,inductance, 1st year stuff only 20 questions.
Safe isolation it's piss easy just keep testing for potentially live and keep checking your testers, keep talking yourself though every process and pretend that the fuseboard is in another room.
Start stop motor circuit is a dodle just follow the drawing you can't go wrong.
Hope this helps.
Also met some nice guys there good luck to them
All the best
Shaun
#12
Forum Regular
Joined: Feb 2011
Location: Egremont, Cumbria
Posts: 59
Re: vetasses practical tools?
Hello Shaun,
Nice to meet you on Monday mate. Like you said Dean was more than helpful, and gave us some info on how the system works now the points system has changed on July 1st. He said that ALL sparks, after entering Oz, must do the gap training and this also means WA, which mucks my plans up of doing it in 4 months. I don't know how hard it will be to get a job over there if your classed as a provisional and need to take time off to go to college to study, or if the unions will need to tell the companies that this is the way forward.
Like he was saying, theres the forcast of AU$250-400billion worth of work to come off over there in the mining and oil/gas industry so surely the companies will need to take provisionals on board.
Cheers
biggaf.
p.s. Before I wipe them off my computer I have pdf files of the intallation calculations books(vols I and II) plus the Cambridge IELTs 7 revision book on pdf file. I only used these books for revision and they were well needed!!
p.m. me if anybody wants them, cos they'll be off the system in a few days.
Nice to meet you on Monday mate. Like you said Dean was more than helpful, and gave us some info on how the system works now the points system has changed on July 1st. He said that ALL sparks, after entering Oz, must do the gap training and this also means WA, which mucks my plans up of doing it in 4 months. I don't know how hard it will be to get a job over there if your classed as a provisional and need to take time off to go to college to study, or if the unions will need to tell the companies that this is the way forward.
Like he was saying, theres the forcast of AU$250-400billion worth of work to come off over there in the mining and oil/gas industry so surely the companies will need to take provisionals on board.
Cheers
biggaf.
p.s. Before I wipe them off my computer I have pdf files of the intallation calculations books(vols I and II) plus the Cambridge IELTs 7 revision book on pdf file. I only used these books for revision and they were well needed!!
p.m. me if anybody wants them, cos they'll be off the system in a few days.
#13
Forum Regular
Joined: Nov 2009
Posts: 48
Re: vetasses practical tools?
"He said that ALL sparks, after entering Oz, must do the gap training and this also means WA, which mucks my plans up of doing it in 4 months."
Hi Biggaf, does this gap training only concern the sparkie's that enter after july 2011.
Regards
Deanc
Hi Biggaf, does this gap training only concern the sparkie's that enter after july 2011.
Regards
Deanc
#14
Forum Regular
Joined: Feb 2011
Location: Egremont, Cumbria
Posts: 59
Re: vetasses practical tools?
I think so, but maybe someone could clarify this who knows a bit more about it.
#15
Re: vetasses practical tools?
steve