Maximum demand, Please explain.

Maximum demand, Please explain.

Old Jun 14th 2010, 5:29 am
  #1  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Maximum demand, Please explain.

Have been trying to work this out and as much as i can get most of it. Some things still confuse me. Ok from the PEER workbook Appendix C worsheet D.

Determine the maximum demand of a single domestic electrical installation supplied with single phase having the following load.


19 lighting points
6 10A double socket outets
16 single socket outlets
1 15A socket outlet
1 20A socket outlet
3 50W exaust fans
3 1000W strip heaters
12.4kW range
1 4.6kW instantaneous water heater
4 500W lights for tennis court

Ok heres what i undertsand

Load group A(i) 19 lighting points= 3A
3X 50W exaust fans = 135? points going from an example in the regs
So 3+2+2+2=9?

Load group A(ii) 500W lights = non applicable?
Load group B(i) 6 double sockets+16 single sockets =22points?
3 x 1000W strip heaters = 3points(using another example in the book ie 1point for one 1000W heater.) where is this info?
Load group B(ii) 1 x 15A socket outlet = 10A?
Load group B(iii) 1 x 20A socket outlet = 15A?
Load group C 12.4kW range = _____ x 05=______Where do i get this info?
Load group F - water heater 4.6W = ____A?

I hope this makes sense to someone. Help please.
Jockstar is offline  
Old Jun 14th 2010, 11:26 am
  #2  
BE Enthusiast
 
Lee and Joanne's Avatar
 
Joined: Apr 2007
Location: O'Halloran Hill, Adelaide
Posts: 414
Lee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really niceLee and Joanne is just really nice
Default Re: Maximum demand, Please explain.

Originally Posted by Jockstar
Have been trying to work this out and as much as i can get most of it. Some things still confuse me. Ok from the PEER workbook Appendix C worsheet D.

Determine the maximum demand of a single domestic electrical installation supplied with single phase having the following load.


19 lighting points
6 10A double socket outets
16 single socket outlets
1 15A socket outlet
1 20A socket outlet
3 50W exaust fans
3 1000W strip heaters
12.4kW range
1 4.6kW instantaneous water heater
4 500W lights for tennis court

Ok heres what i undertsand

Load group A(i) 19 lighting points= 3A correct +2A for fans =5A
3X 50W exaust fans = 135? points going from an example in the regs
So 3+2+2+2=9?read footnote c in notes to table c1-add to lights

Load group A(ii) 500W lights = non applicable? .75% OF CONNECTED LOad 6.25A
Load group B(i) 6 double sockets+16 single sockets =22points?
3 x 1000W strip heaters = 3points(using another example in the book ie 1point for one 1000W heater.) where is this info? FOOTNOTE(i)lees than 10A add to B
Load group B(ii) 1 x 15A socket outlet = 10A?}footnote (J)
Load group B(iii) 1 x 20A socket outlet = 15A?
Load group C 12.4kW range = _____ x 05=______Where do i get this info? 12400/230 =53.9A 54A x 50% 27A
Load group F - water heater 4.6W = ____A? 4600/230 x 33.3%= 6.66A

I hope this makes sense to someone. Help please.
does this make sense
Lee and Joanne is offline  
Old Jun 14th 2010, 2:22 pm
  #3  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Originally Posted by Lee and Joanne
does this make sense
Hi ,

Please clarify where did you get 2amps for fan.

I assume that 19 lights plus 3 x 50w fan

total 22 lights = 3A + 2A.

is this correct.

please give a feed back

will be appreciated.
thanks
Askar is offline  
Old Jun 16th 2010, 8:30 am
  #4  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Originally Posted by Askar
Hi ,

Please clarify where did you get 2amps for fan.

I assume that 19 lights plus 3 x 50w fan

total 22 lights = 3A + 2A.

is this correct.

please give a feed back

will be appreciated.
thanks
Askar is offline  
Old Jun 16th 2010, 8:39 am
  #5  
mcv
Forum Regular
 
mcv's Avatar
 
Joined: Jul 2008
Location: Scoresby,Melbourne
Posts: 84
mcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nicemcv is just really nice
Default Re: Maximum demand, Please explain.

yes that is correct
mcv is offline  
Old Jun 16th 2010, 8:48 am
  #6  
Just Joined
 
Joined: Dec 2008
Posts: 23
shrikrishan is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Can neone plz tell that how many questions in total comes in wiring rule exam in peer
shrikrishan is offline  
Old Jun 16th 2010, 1:36 pm
  #7  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Thanks mate.
Askar is offline  
Old Jun 17th 2010, 6:58 am
  #8  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Lee and Joanne
does this make sense
Sort of. I dont get this.

Load group A(ii) 500W lights = non applicable? .75% OF CONNECTED LOad 6.25A
Jockstar is offline  
Old Jun 17th 2010, 7:12 am
  #9  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

Its 4 X 500w = 2000/230 x .75 = 6.25.

hope that explains.
Askar is offline  
Old Jun 17th 2010, 7:17 am
  #10  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Jockstar
Have been trying to work this out and as much as i can get most of it. Some things still confuse me. Ok from the PEER workbook Appendix C worsheet D.

Determine the maximum demand of a single domestic electrical installation supplied with single phase having the following load.


19 lighting points
6 10A double socket outets
16 single socket outlets
1 15A socket outlet
1 20A socket outlet
3 50W exaust fans
3 1000W strip heaters
12.4kW range
1 4.6kW instantaneous water heater
4 500W lights for tennis court

Ok heres what i undertsand

Load group A(i) 19 lighting points= 3A
3X 50W exaust fans = 2A total 3+2 = 5A

Load group A(ii) 500W lights = Still not sure how you get that.
Load group B(i) 6 double sockets+16 single sockets =22points?
3 x 1000W strip heaters = 3points= 22+3=25points so 10A+5A=15A?
Load group B(ii) 1 x 15A socket outlet = 10A
Load group B(iii) 1 x 20A socket outlet = 15A + base loading of 15A= 40A?

Load group C 12.4kW range = 12400/230= 53.9(54) 54x 0.5= 27A
Load group E - water heater 4.6W = 4600/230= 20A x 0.33= 6.66A

I hope this makes sense to someone. Help please.
Ok. Before i move on to the next one in the book. I want to make sure i understand this and have it right. I have changed the above to what i think it has to be now. Sorry if it seems like I'm being stupid. But i just cant see it sometimes. Once its pointed out. Its the light bulb going on.
Jockstar is offline  
Old Jun 17th 2010, 7:29 am
  #11  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Askar
Its 4 X 500w = 2000/230 x .75 = 6.25.

hope that explains.
Ah! Ok. I forgot it was times 4. lol Does the rest look right?
Jockstar is offline  
Old Jun 17th 2010, 7:33 am
  #12  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Jockstar
Ah! Ok. I forgot it was times 4. lol Does the rest look right?
Load group A(i) 19 lighting points= 3A
3X 50W exaust fans = 2A total 3+2 = 5A

Load group A(ii) 500W lights = 4 x 500W = 2000W/230 x 0.75 = 6.5A
Load group B(i) 6 double sockets+16 single sockets =22points?
3 x 1000W strip heaters = 3points= 22+3=25points so 10A+5A=15A?
Load group B(ii) 1 x 15A socket outlet = 10A
Load group B(iii) 1 x 20A socket outlet = 15A + base loading of 15A= 40A?
Load group C 12.4kW range = 12400/230= 53.9(54) 54x 0.5= 27A
Load group E - water heater 4.6W = 4600/230= 20A x 0.33= 6.66A

So overall total would be 100A?
Jockstar is offline  
Old Jun 17th 2010, 9:05 am
  #13  
Just Joined
 
Joined: Jun 2010
Posts: 25
Askar is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

The rest is right except, Group B(iii) is 1x 20 amps socket = 15amps

Total demand is about 85.15amps.
Askar is offline  
Old Jun 17th 2010, 11:06 am
  #14  
Freedom!
Thread Starter
 
Jockstar's Avatar
 
Joined: Nov 2004
Location: At home in Sydney. Ye!!!!
Posts: 1,697
Jockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond reputeJockstar has a reputation beyond repute
Default Re: Maximum demand, Please explain.

Originally Posted by Askar
The rest is right except, Group B(iii) is 1x 20 amps socket = 15amps

Total demand is about 85.15amps.
Ok thanks. will attempt the next sheet maybe tomorrow and post back here to see if I'm right.
Jockstar is offline  
Old Jun 17th 2010, 9:20 pm
  #15  
Just Joined
 
Joined: Dec 2008
Posts: 23
shrikrishan is an unknown quantity at this point
Default Re: Maximum demand, Please explain.

The correct answer is 95.16 amps